Hi,
earth leakage detection device = ground fault circuit interruptor protection device. I'm on 220V AC.
The old office building where I'm located has recently started installing one earth leakage detection device for several users.
As expected, when someone brings in a 'leaky' device, all users on the circuit are punished ! I moved my computer on to the light circuit which seldom loses power.
It seems to me that domestic usage of earth leakage detection doesn't apply to 'commercial'/office block usage ?
For domestic:
- the owner knows and controls all the devices,
- the 30 mA is probably based on an average fatal dosage ?
- they assume that the rest of the 'devices' total to < 10 mA ?
So what if the circuit has already got several devices whit a total leakage accumulate to 25 mA. And even if 6 mA is not consdered a problem, you still get a power-out for all the clients !
It seems to me that you need a 'delta' [rate of change] measurement of the imbalance of the live and neutral currents. It's realistic to assume that not 2 or more outlets will develop a fault at the same time [except at initial power-up]. So if XmA is the critical/dangerous current, even if the total leakage has accumulated to say 5X mA, a further change of +0.5X mA doesn't justify a power-down.
Do such devices exist ? I read via google 'self tuning' earth leakage detection devices; what is that ? What is the proper method, when say 10 offices are on one switchboard ?
Thanks for any info.
== Chris Glur.