| I am installing a subpanel in my woodshop. I need at the minimum a 30 | A circuit. The run from subpanel to shop is less than 50 feet so | voltage drop is well within tolerance. | | I was thinking of pulling either 6 or 8 gauge cable and I have two | questions: | 1) Would you use 6 or 8 gauge or stick with 10 gauge?
#6
| 2) Is 6 or 8 gauge a pain in the butt to work with at the main panel?
only slightly more than the smaller gauge
| Also, any war stories on your panel installs would be appreciated.
Often I hear of additional capacity being needed once electricity is there. So I'd suggest #6 or even #4 and going with a 60 amp subpanel (a common size anyway). If the subpanel has a 60 amp (or less) main breaker of its own, then you can feed the #4 with 70 amp (or maybe more if the wire is rated for a higher temperature ... see NEC wire tables). If the subpanel is "main logs only" then feed it with a 60 amp breaker in the main box.