I have a question from a neighbor who asked me why this won't work. He has identified 2 circuits he wants to switch over to a generator. The plan is to break the cable to the circuit(s) where it exits the service panelboard and install a device box. Put in a single pole double throw switch with the common to the load side of the circuit, one switch leg to the panel O/C device and the other to the male socket that he would connect a generator cord to. (one for each circuit). The only issue I can see is the location of the bonding jumper. If the generator has a bonding jumper I suppose you should also be switching the neutral (DPDT switches) but other than that I am having a problem finding a problem. I have even had inspectors say that is not a problem (2 bonding jumpers, one in the separately derived source, since the load is downstream of the grounding point). What do you guys think?