Three Phase Converter Question

I've got a working 7.5 HP idler running a true 5 HP (24 amp draw) 120 gallon air compressor plus my Bridgeport and a couple of other smaller motors. This motor runs on a 40 amp breaker out of a 200 amp main. I need to increase my service to accommodate a three phase welder. Is it possible to add another motor in the circuit rather than build a new larger system from scratch. My idea is to break the circuit between the

existing 7.5 HP idler and the air compressor/ mill and drop each of the

three legs down to a disconnect. Then from the disconnect wire the three legs into a larger motor which would feed the welder when needed but would be dropped from the circuit when not using the welder. The welder requires about 35 amps line input and outputs 250 amps at 100% duty cycle. Anyone with experience with this? I'm not sure this is feasible. I'm unsure of how big of a 'secondary idler' I'll need and unsure of how big of a motor the 7.5 HP 'primary idler' will start. What will this do

to my feed from the main to the 7.5 HP motor? Will I need to increase the wire size and breaker size from the 7.5 HP motor to the 200 Amp main service, or should I wire the larger motor as the primary Idler straight from the 200 Amp Main and use the 7.5 to supply the additional

power for the welder? All comments/suggestions welcome. Best regards

"Suppose you were an idiot. And suppose you were a member of Congress..

But I repeat myself."

--Mark Twain

Reply to
Lefty
Loading thread data ...

Lefty, i am very confused. is you main service single phase and all your equipment 3 phase running on rotary converter(s) ?

Reply to
TimPerry

Reply to
Lefty

ok, i think i see what you have, however i have no particular expertise or experience with this. i would use a true rotary converter (motor/generator set) for this application. i have been at one mountain top location that had several running simultaneously.

Reply to
TimPerry
25,000 kVA??? Wow, that transformer must be as big as your house! You probably meant 25kVA which is 25,000VA, but I couldn't resist poking fun at your mistake.

If you go to www.practicalmach>Yes, my main is a 200 Amp regular residential service coming off a

Reply to
Bob Ferapples

You're right. I had way too many zeros in the equation.