voltage drop ?

Dec 17, 2005 4 Replies

First reply

Don Kelly

You can measure the voltage at each end of the loaded circuit and find the difference. Measuring at no load would be meaningless.

Read the full reply

can VD actually be measured at the end of a circuit while the amp load is on?Using a DMM. Is this a accurate way to measure for voltage drop?thankyou



You can measure the voltage at each end of the loaded circuit and find the difference. Measuring at no load would be meaningless.

What about measuring open-circuit voltage (no load) and then voltage under a known load? You can not only determine the voltage drop due to a reference load (e.g., 15 or 20 amps) but the circuit resistance as well. Isn't this pretty much what the Ideal testers do?

Chuck

its easy to calculate vd = I*L*mV/A/m (mV/A/m = drop per amp per metre found in the regs book) ------------------- 1000

--------- It comes to the same thing in theory but is more convenient (measuring at one point only) than my suggestion.

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required