wiring capacity question

I have a 240v (single phase) outlet in my garage with a 30 amp breaker (10/3 wire) that I use for my miller 175 mig welder (230v 19.5amp @60hz) and I
wanted to upgrade my compressor to a 240v 15amp model. I realize that if both are running off that breaker I will exceed the 30 amps by 4.5 amps. My question is will it still work based on the fact that I seldom fire up the mig welder to it's highest setting and run the compressor at the same time? thanks in advance. walt ps. I'm hoping to change my panel over to a higher service, then run another 230 line out so that it would solve these problems in the future.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

Welders are seldom used to thier full capacity. Usually 70% is a good figure unless you are in a industrial type enviorment. Set your welder to your highest USED rating, turn on the compressor and test weld. The breaker may/may not trip. If you have access to an ampmeter, test the amps of the load at that point. Also, unless the breaker is bolt-in type you want to limit your load to 70% of the rating of the breaker. Manufacturers claim all thier breakers are 100% rated but pactically, run one at 100% continuosly and see how long it lasts!
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wallsterr wrote:

Its not quite per code. They won't grant you an allowance for diversity between these two units. But for your own peace of mind, you could rig up some sort of interlock such that the compressor would be shut off when the welder is drawing power.
You probably don't want the compressor to fire up in the middle of a weld on the off chance that the combination might trip the breaker.
--
Paul Hovnanian mailto: snipped-for-privacy@Hovnanian.com
note to spammers: a Washington State resident
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
and I

My
time?
another
As long as the compressor and the welder are not running at the same time then you will be fine. You might not need to upgrade your service. Just run another 10/3-10/4 line to the garage. Same thing applies, you are not welding/air compressor and your wife is not running the dryer and/or oven at the same time. I connected a friends home to a 100 amp service for the well. He ran 3 years before we actually got the home connected. I back fed the service on the house with an 100 amp breaker. Since my wiring was installed in the pipe for the utility there was no danger of anyone being hurt. He did trip the main a couple of times, usually when both a/c's were running and the wife had the oven and or dryer running. He was surprised that there were so few trips. I am sure if there were more we would have gotten around to the utility a lot faster.