Dear jim:
cross-posting to sci.engr.mech
Be very careful. Compressors can be damaged by encountering a snootfull of liquid refrigerant on the intake. Increasing the cooling here would be counterproductive.
I think you need to review your basic cycles. On a refrigeration cycle:
1) gaseous refrigerant is drawn in and compressed, 2) the hot refrigerant gas is cooled across a condensor, 3) the warm refrigerant liquid has its pressure dropped across an orifice ("expansion valve"), 4) the cold refrigerant gas absorbs heat through the evaporator.Increasing the effective size of the condensor will make your unit more efficient. But only to a point. Only so much liquid can go through the expansion valve, and a 2 deg difference in this liquid means very little additional cooling.
Keeping the correct pressures for the ambient-to-cold-space temperature difference will make it more efficient also.
I'd look at more efficient insulation, and leave the refrigeration cycle alone. You never know the damage you can do, or the quality of the person you will call in to service it.
David A. Smith