You can't -- but there are 240 V rated ones with a center tap so you can feed them from 120 V and still get the whole range.
But hook 240 V across a 120 V rated one (or even one of the over-range ones which can go to 140 V) and you will probably fry the fuse in series with the line input (if you put a proper rating on the fuse, of course. :-)
BTW I remembered another thing to consider when wiring up these (both single input voltage and the the double trick to get 240V coverage from two 120 V ones).
Use *two* fuses per variable autotransformer -- one at the input, and one at the wiper output. The first protects you from too much current going in when you have an overrange one set to produce more output voltage than the input, and the second protects you when you are putting out less voltage (often much less) than the input.
The current rating is based on what the wire in the winding will handle, and depending on the setting, you get more current at the input or at the output, so protect both.
Indeed so. These won't have overvoltage ranges, but still need fuses at both input and output to be truly safe.
Enjoy, DoN.