Rigid Conduit vs Regular Iron pipe

Can any one tell me what the difference between rigid conduit and iron pipe? inner finish threads on the pipe and in the fittings and any other
significant differences. TIA
CP
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

You can bend conduit with an inexpensive tool. Conduit is much lighter and cheaper than pipe.
Dan
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 3/1/2013 6:40 PM, snipped-for-privacy@krl.org wrote:

I've never seen rigid bent, only light & intermediate. Rigid is heavy & threaded. It uses preformed sweeps & boxes to make turns. AFAIK
Bob
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Fri, 01 Mar 2013 19:31:04 -0500, Bob Engelhardt

Only if you dont have a pipe bender for rigid. I have several differnet types of hand benders for rigid.
Gunner
The methodology of the left has always been:
1. Lie 2. Repeat the lie as many times as possible 3. Have as many people repeat the lie as often as possible 4. Eventually, the uninformed believe the lie 5. The lie will then be made into some form oflaw 6. Then everyone must conform to the lie
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Gunner wrote:

Rigid is fun to bend. You definately need more thean a three foot handle on the bender. Have you ever used rigid aluminum conduit?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 02 Mar 2013 15:11:02 -0500, "Michael A. Terrell"

Ive heard of aluminum conduit..but give its properties...Id stay way way away from it.
I did help install a hydrogen furnace (50 feet long) using stainless steel 1" pipe some years ago though. Some really odd pipe dope in that project.
Gunner
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Gunner wrote:

They used it in a juice processing plant near here, along with a lot of stainless pipes for the juice. I ended up with some leftover 3/4" aluminum conduit that had surface damage.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sun, 03 Mar 2013 01:26:04 -0500, "Michael A. Terrell"

Whats it like to bend and how is the surface treated? Sounds like White Fur country. That nasty white fur that grows on unanodized aluminum as it eats its way in.....
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Gunner wrote:

The stuff is soft compared to iron. It can be bent by hand, and has anodized surface. I had about 40 to 45 pieces, till my dad found it in my stockpile and bent it into a pile of scrap to sell for the aluminum. I had told him he could use any of the EMT scraps he wanted, but to leave all the 10' pieces alone. He wasted about $1000 worth of pipe & conduit.
I only manged to find a few pieces he missed. He would step on it in the middle and fold it in half. It brought about 15% of the price it would have sold for as conduit.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sun, 03 Mar 2013 19:48:43 -0500, "Michael A. Terrell"

OUUUCHH!!!!!
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
I've bent miles of rigid pipe
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Fri, 1 Mar 2013 15:40:45 -0800 (PST), " snipped-for-privacy@krl.org"

Conduit is thin wall material. It cant be threaded with any suitability. Its not designed to carry anything other than wire.
Pipe is thick wall and is designed to be threaded and then threaded into pipe fixtures...
Its capable of carrying significant pressures
Gunner
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

You are thinking EMT - electro-metalic tubing - not Rigid Conduit. Rigid conduit is thick, and is threaded for EVERY use. 1" rigid conduit is .126 inch wall. The thread is generally a straight thread instead of a tapered thread on pipe. 1 inch Sched 40 iron pipe is .130" wall thickness. 2 inch rigid is .146 inch wall thickness, while sched 40 iron is .150 nominal thickness
Rigid steel conduit can be galvanized (in and out) electro galvanised (outer only) with organic coated interior, or organic coated in and out - and Rigid conduit can also be aluminum or stainless steel or red brass.
RMC has a smoother interior than pipe - it is a rolled, electrically welded seam tubing with uniform wall thickness and a defect free interior surface - required for pulling wire.
Black Iron Pipe is made from ductile iron - not steel (generally speaking).

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 02 Mar 2013 15:08:28 -0500, snipped-for-privacy@snyder.on.ca wrote:

You are absolutely correct. I glossed over the first "rigid" My appologies indeed.
A definate Brain Fart on my part.
Gunner

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 3/1/2013 3:11 PM, Pilgrim wrote:

There are three standard weights for electrical conduit -- EMT ("thinwall"), IMC (intermediate metal conduit) and GRC (galvanized rigid conduit). Partial table of standard dimensions per relevant ANSI spec's...
GRC
MIN. WGT. /100 FOOT O.D. I.D. THICKNESS SIZE IN LBS. INCHES INCHES INCHES 1/2" 79 0.840 0.632 0.104      3/4" 105 1.050 0.836 0.107 1" 153 1.315 1.063 0.126 1 1/4" 201 1.660 1.394 0.133 1 1/2" 249 1.900 1.624 0.138 2" 332 2.375 2.083 0.146
EMT
1/2" 29 0.706 0.622     0.042 3/4" 44 0.922 0.824 0.049 1" 65 1.163 1.049     0.057 1 1/4" 96 1.510 1.380 0.065 1 1/2" 111 1.740 1.610 0.065 2" 141 2.197 2.067 0.065
Steel pipe Sch Sch Sch Sch OD 5 10 40 80 1/2 0.840 0.065 0.083 0.109 0.147 3/4 1.050 0.065 0.083 0.113 0.154 1 1.315 0.065 0.190 0.133 0.179 1 1/4 1.660 0.065 0.109 0.140 0.140 1 1/2 1.900 0.065 0.109 0.145 0.200 2 2.375 0.065 0.109 0.154 0.218
As can be seen, GRC is roughly same weight as, but still slightly lighter (thinner wall) than Sch 40 pipe but they have same OD
--


Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Thanks for your informative reply. What are the thread specs? Std NPT or something else. The couplings I have seen for GRC seen to be non tapered. Is GRC meant to be liquid tight to prevent moisture entering? Thanks
CP
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

GRC uses a NPS thread, not NPT (National Pipe Straight) not (National Pipe Tapered)
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 02 Mar 2013 15:11:34 -0500, snipped-for-privacy@snyder.on.ca wrote:

I think this misunderstanding has been repeated here several times. The threads on the ends of rigid conduit are tapered pipe threads. Female threads on conduit fittings are often straight threads.
Per Wheatland: "Wheatlands Galvanized steel Rigid Metal Conduit (RMC) is manufactured in accordance with the latest specifications and standards of ANSI C80.1, UL-6, and federal specification WW-C-581. The pitch of RMC threads conforms to the American National Standard for Pipe Threads, General Purpose (Inch), ANSI/ASME B1.20.1. The taper of threads is 3/4 inch per foot (1 in 16). "
From NFPA 70 - 2008: "344.28 Reaming and Threading. All cut ends shall be reamed or otherwise finished to remove rough edges. Where conduit is threaded in the field, a standard cutting die with a 1 in 16taper (3/4-in. taper per foot) shall be used. FPN: See ANSI/ASME B.1.20.1-1983, Standard for Pipe Threads, General Purpose (Inch)."
--
Ned Simmons

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Thanks. This is the info I was looking for.
CP
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sunday, March 3, 2013 at 9:12:58 AM UTC+7, Ned Simmons wrote:

r

d.


A53 (grade A) and buried it in concrete as electrical rigid conduit. Rigid conduit comes according to ANSI C-80.1
Can this steel pipe installed be threaded or made compatible with "real" ER SC pipe?