Certainly the statement from any utility 'it couldn't happen' should be treated with contempt - they don't monitor each customer premises and we have had similar problems while the wires were overhead. I anticipate that it might happen again. At least once told they DID switch of the feed rather than giving a 'dangerous' answer, and I suspect any adviser who made that sort of statement should be retrained?
Didn't find your answer? Ask the community — no account required.
Yes. But testing your process and finding out its characteristics, hopefully...
M
mark
...pah! 16mm 4 core - baby stuff 160 amps per phase three phase
pah! 120mm 4 core - baby stuff.
185mm - 4 core-315 amps a phase
Mark.
A
Andrew Mawson
Swank
AWEM
J
Julian
We are single phase. We have a single phase 11KV (I think it's 11KV) supply to a transformer mounted up a pole in the garden, this transformer supplies just me and the neighbour from its single phase output. I think the root cause of the problem is this antiquated transformer which almost certainly dates back to the days when national grid electrickery first found it's way out into the countryside.
I've never seen anything like 240 volts - chance would be a fine thing :-) I'll be contacting MANWEB on Monday morning to see what they say on the issue.
I don't think the board's cable from the transformer to the meter is much more than 6mm :-(
Regards Julian.
J
John S
I'll bet you get brownouts in Bradford.
John S.
C
Charles
But your factory is about 10 times the size of my house, garden, neighbours house, their garden and the road inbetween!
Charles
M
Mark Rand
Could do with one in Downing Street...
Mark Rand RTFM
G
Graham
The document you want is "The Electricity Safety, Quality and Continuity Regulations 2002"
formatting link
There has been updates since but only to update references from the
16th regs to the 17th regs.
From page 14
(3) For the purposes of this regulation, unless otherwise agreed in writing by those persons specified in paragraph (2), the permitted variations are? (a) a variation not exceeding 1 per cent above or below the declared frequency; (b) in the case of a low voltage supply, a variation not exceeding 10 per cent above or 6 per cent below the declared voltage at the declared frequency; (c) in the case of a high voltage supply operating at a voltage below
132,000 volts, a variation not exceeding 6 per cent above or below the declared voltage at the declared frequency; and (d) in the case of a high voltage supply operating at a voltage of
132,000 volts or above, a variation not exceeding 10 per cent above or below the declared voltage at the declared frequency.
note: low voltage =< 1000 v rms AC
mmmm, electricity suppliers...... Good luck
It is not uncommon at all to see lights dim / flouresants flash when heavy loads are switched on. Electric showers and banks of downlighters are particually good at that.
Also, the regs on volt drop within an installation have changed for the 17th edition. It used to be 4% (9.2v) max. it has changed to 5% (11.5v) for general circuits and 3% (6.9v) for lighting.
In the regs there is a general requirement to install under voltage protection (this includes temporary loss of supply) where it may cause harm (section 445), for example a motor overheating, or an item stopping and restarting unexpectedly. In practice all consumer goods will be tested and suitable devices inbedded within, such as a thermal fuse or an interlock on a food mixer preventing you from getting at the moving blade should it restart. So this requirement can be largely ignored, and could itself cause danger if not properly applied, such as having to reset a trip in the dark. I have only come across dedicated units on large industrial stuff, with no-volt releases (Motor starters) providing enough protection for smaller motors / items.
Graham
J
Julian
Thanks the lot Graham for the reply, very helpful indeed.
Julian.
Join the Discussion
Have something to add? Share your thoughts — no account required.
Didn't find your answer?
Ask the community — no account required
Report Content
You are reporting this content to the moderators. They will look at it
ASAP.