I've been researching a problem in non-linear control and I've come up with a problem that seems rather easy but nevertheless have not been able to tackle it. Any help is appreciated. Here goes:
Let x'=f(x,u) be a non linear system. The controls uEU (where U is a bounded subset of R^m, i.e. the controls are bounded. "E" denotes the "belongs to" operator). Suppose you have a stabilizing feedback law u(x) such that x->0 (with f(0,0)=0 being an equilibrium point). Now consider that you change the bounds of the control space through a transform F(U)=U' such that 0EU' and the intersection of U and U' is not empty. And the question is: Does the control u(x) still stabilizes the system? Or, more strictly speaking, does the feedback law s(u(x)), where s is a saturation function that cuts off u(x) when it exceeds the bounds of U', stabilizes the system?
Didn't find your answer? Ask the community — no account required.
The simple answer is use an on-off switch unless you are willing to add...
J
JCH
schrieb im Newsbeitrag news: snipped-for-privacy@h2g2000hsg.googlegroups.com...
If you have a 'real' example (F1(s), F2(s), etc.) I could try to solve it. Then you could compare your results with the results I found. My program can handle nonlinear differential equations.
T
Tim Wescott
If I read your rather terse math correctly, the general answer is "maybe", as in "sometimes, depending". In other words, depending on the plant, the control law, and your changes to the bounds, you may or may not end up with something stabilizing.
As an example, consider a load that is pivoted on bearings and driven by a torquer motor. The response of the system in position will be a double integral of the torque command. Now drive this with a PID controller. I'll assume that by "unstable" you mean that the phase space of the system contains limit cycles in response to constant inputs, not that the system has unbounded responses.
If you just tune the controller as if the plant is linear, with no nonlinear compensation at all, but you bound the torque to some maximum absolute value such as you'd see with just about any real system, your system will have a hard limit cycle in closed loop. It will be perfectly stable and well behaved for small excursions, but if you put it into a state where the controller is demanding more torque than the torquers will supply then the system will go into oscillation.
You can correct this problem by arranging your controller such that it limits the velocity command, treating it as a proportional loop wrapped around a PI loop with velocity feedback (see figure 8.16 on page 215 of my book for a simplified example). With a simple 3-segment piecewise linear velocity command limiting you'll achieve stability, with more sophisticated velocity command limiting you'll bring the system to a rest with maximum torques being exerted for all but the very end of the move.
Note that this controller must have nonlinearities that are sized to the torque limits. So take the system, and reduce the torque limits significantly. At some point (in practice probably between a 2x and a
10x reduction) you'll find that you can once again observe a hard limit cycle, so you've lost stability.
On the other hand, increase the torque limits by any factor you want. Your system will remain stable, although it will not drive the torquers to their maximum effort.