208 volt UPS

A UPS is rated to normally operate on 208V, but can be configured to operate also on 200V, 220V, 230V, and 240V. It comes with NEMA 6-30P plug and has NEMA 6-20R x2 and NEMA 6-30R x2 outlets. These are standard for USA 208/240 volt circuits that have no neutral connection.

What system type would you expect such a UPS to output when it is configured for each of the voltages (200, 208, 220, 230, 240)? Would you expect each hot wire, when measured relative to ground (not neutral since there is no neutral) to be 50% of the L-L voltage and a phase angle of 180 degrees, or

57.7% of the L-L voltage and a phase angle of 120 degrees? Would you expect the phase angle (and hence L-L : L-G ratio) to be different with different voltage settings?

If it ONLY had voltage choices of 208 and 240 I could believe it might do this by keeping the L-G voltage at 120 and varying the phase angle. But with the other voltages being an option, I'm not so sure. While any of those voltage could be derived from selected phase angles of 120 volts, I would expect that to actually be an odd thing to do.

I'm curious if such a unit could be run on 208V input (two phases in a

208Y/120 system) and 240V output reasonably (it can apparently be set to do that so I would think the vetted the design for it). I'm just not sure what kind of system I'd be getting (120/240 at 180 degrees or 139/240 at 120 degrees). Given that it has no neutral, clearly they are not expecting any L-N loads. But some devices could, in theory, monitor a L-G voltage and treat 139 volts as overvoltage.

I am currently looking at the APC model SURT5000RMXLT.

Reply to
phil-news-nospam
Loading thread data ...

Given the info provided, and our experience testing UPS, I think they UPS will produce neither the 120/208 or 240 split phase. It will produce the Line to Line voltage that is selected. The relationship to ground will NOT be part of that output. There is a ground, and it will be somewhere in relation to the output voltage but there will be NO attempt by the UPS to maintain a certain phase angle relationship. The output inverter will NOT even use the ground. So, the voltage measured from each Line to ground could be anywhere from full rated voltage to zero, and may not be fixed.

Charles Perry P.E.

Reply to
Charles Perry

|> What system type would you expect such a UPS to output when it is |> configured |> for each of the voltages (200, 208, 220, 230, 240)? Would you expect each |> hot wire, when measured relative to ground (not neutral since there is no |> neutral) to be 50% of the L-L voltage and a phase angle of 180 degrees, or |> 57.7% of the L-L voltage and a phase angle of 120 degrees? Would you |> expect |> the phase angle (and hence L-L : L-G ratio) to be different with different |> voltage settings? |>

| | Given the info provided, and our experience testing UPS, I think they UPS | will produce neither the 120/208 or 240 split phase. It will produce the | Line to Line voltage that is selected. The relationship to ground will NOT | be part of that output. There is a ground, and it will be somewhere in | relation to the output voltage but there will be NO attempt by the UPS to | maintain a certain phase angle relationship. The output inverter will NOT | even use the ground. So, the voltage measured from each Line to ground | could be anywhere from full rated voltage to zero, and may not be fixed.

Hmmm. So if multiple UPSes connect multiple pieces of equipment, and those multiple pieces of equipment are interconnected to each other by ground and signals (a room full of computers), this could produce strange voltages in the network? ... like as much as 416 volts? ... or maybe more?

I think I'd rather have a fully grounded system, but with a 30ma GFI to block attempts to use the grounding wire as a current conductor.

Reply to
phil-news-nospam

| |> What system type would you expect such a UPS to output when it is | |> configured | |> for each of the voltages (200, 208, 220, 230, 240)? Would you expect each | |> hot wire, when measured relative to ground (not neutral since there is no | |> neutral) to be 50% of the L-L voltage and a phase angle of 180 degrees, or | |> 57.7% of the L-L voltage and a phase angle of 120 degrees? Would you | |> expect | |> the phase angle (and hence L-L : L-G ratio) to be different with different | |> voltage settings? | |>

| | | | Given the info provided, and our experience testing UPS, I think they UPS | | will produce neither the 120/208 or 240 split phase. It will produce the | | Line to Line voltage that is selected. The relationship to ground will NOT | | be part of that output. There is a ground, and it will be somewhere in | | relation to the output voltage but there will be NO attempt by the UPS to | | maintain a certain phase angle relationship. The output inverter will NOT | | even use the ground. So, the voltage measured from each Line to ground | | could be anywhere from full rated voltage to zero, and may not be fixed. | | Hmmm. So if multiple UPSes connect multiple pieces of equipment, and those | multiple pieces of equipment are interconnected to each other by ground and | signals (a room full of computers), this could produce strange voltages in | the network? ... like as much as 416 volts? ... or maybe more? | | I think I'd rather have a fully grounded system, but with a 30ma GFI to | block attempts to use the grounding wire as a current conductor.

I've started getting some answers from their tech support. After a couple back and forth they finally asked an engineer, and passed on the statement that it is possible for one leg to be 120V and the other to be 88V relative to ground. Now that is odd.

If you were DESIGNING a UPS, part of a series of different models for many different needs, with THIS model intended to serve cases where power comes in on a NEMA-6 (at whatever amperage), at either 208V in cases where three phase is the mains supply, or 240V in cases where single phase is the mains supply, and it needs to be double conversion continuous on-line type, how would you design it?

Reply to
phil-news-nospam

Why do I care about the relationship between the ground and the two "hot" conductors? As long at the line to ground voltage never exceeds the line to line voltage why do I care? You should never connect a load from line to ground. On this type of UPS the load has to be connected line to line. As long as the line to line voltage stays in spec, what does it really matter? Without an output isolation transformer the UPS does NOT qualify as a separately derived source, so you would never bond the ground to either Line.

Charles Perry P.E.

Reply to
Charles Perry

|> If you were DESIGNING a UPS, part of a series of different models for many |> different needs, with THIS model intended to serve cases where power comes |> in on a NEMA-6 (at whatever amperage), at either 208V in cases where three |> phase is the mains supply, or 240V in cases where single phase is the |> mains |> supply, and it needs to be double conversion continuous on-line type, how |> would you design it? |>

| | Why do I care about the relationship between the ground and the two "hot" | conductors? As long at the line to ground voltage never exceeds the line to | line voltage why do I care? You should never connect a load from line to | ground. On this type of UPS the load has to be connected line to line. As | long as the line to line voltage stays in spec, what does it really matter? | Without an output isolation transformer the UPS does NOT qualify as a | separately derived source, so you would never bond the ground to either | Line.

It isn't the actual voltage across a line to ground connection that is the issue. The issue is the accumulated phantom voltage between equipment that is interconnected with metallic data lines. In an case with 120/240 mains and equipment connected at opposing poles, the worst case is seeing 240 volts across things. My concern was to make sure I wasn't getting an output that was 208 volts L-G, which could give me a phantom 416 volts across connections between equipment, and possibly outside the normal expectations of insulation in various components.

I do not see how an inverter is not a separately derived system.

If the output is a pair of 120 volt inverters syncronized at either 180 degrees or 120 degrees apart (configurable) to get 240 volts or 208 volts, and these two inverters ARE connected to ground (not neutral as that is not even present), and the load on the inverter is connected line to line, how is this creating a situation for operating current on the ground wire at either the input or output?

Reply to
phil-news-nospam

The code says it is not. There is a bypass switch that can connect the output directly to the input. If you want to qualify as a separately derived source, you have to have a transformer on the output.

Even in normal operating mode, it does not qualify.

It is not a pair of 120V inverters. It is a single 240V inverter that can be programmed to output 208 volts instead (pulse width modulated and filter usually).

Charles Perry P.E.

Reply to
Charles Perry

Where in the code is that?

Not all UPSes have a bypass switch.

| Even in normal operating mode, it does not qualify.

I never saw that in the code.

|> If the output is a pair of 120 volt inverters syncronized at either 180 |> degrees or 120 degrees apart (configurable) to get 240 volts or 208 volts, |> and these two inverters ARE connected to ground (not neutral as that is |> not even present), and the load on the inverter is connected line to line, |> how is this creating a situation for operating current on the ground wire |> at either the input or output? | | It is not a pair of 120V inverters. It is a single 240V inverter that can | be programmed to output 208 volts instead (pulse width modulated and filter | usually).

Then you can have problems with this if the UPS has a bypass switch, since it will change ground reference when the switching happens.

Suppose you do have an isolation transformer on the output. Would you design it so that the secondary winding has a ground tap in the middle, or not?

Reply to
phil-news-nospam

The UPS passes ground straight through. You cannot tie a "line" to ground, it will create a fault. Therefore it is not separately derived. You can try, but I would video tape it as it will be fun to watch after.

The ground goes straight through the UPS.

No. I don't connect a load to ground so if I had a tranformer on the output, I would tie one line to ground. This keeps any leakage current from my load on the output side of the transformer.

I think part of your problem is you keep thinking of UPS in terms of transformers (phase angles between 120 l-g connections to get 208 or 240). Power electronic devices to not have to work like transformers. Once you have a DC bus you can do any thing you want.

Charles Perry P.E.

Reply to
Charles Perry

|> Where in the code is that? |>

|> Not all UPSes have a bypass switch. |>

|>

|> | Even in normal operating mode, it does not qualify. |>

|> I never saw that in the code. |>

| The UPS passes ground straight through. You cannot tie a "line" to ground, | it will create a fault. Therefore it is not separately derived. You can | try, but I would video tape it as it will be fun to watch after.

There is no more of a line tied to ground in the UPS than there is in a transformer producing the same system.

|> |> If the output is a pair of 120 volt inverters syncronized at either 180 |> |> degrees or 120 degrees apart (configurable) to get 240 volts or 208 |> volts, |> |> and these two inverters ARE connected to ground (not neutral as that is |> |> not even present), and the load on the inverter is connected line to |> line, |> |> how is this creating a situation for operating current on the ground |> wire |> |> at either the input or output? |> | |> | It is not a pair of 120V inverters. It is a single 240V inverter that |> can |> | be programmed to output 208 volts instead (pulse width modulated and |> filter |> | usually). |>

|> Then you can have problems with this if the UPS has a bypass switch, since |> it will change ground reference when the switching happens. | | The ground goes straight through the UPS.

As it should. So?

|> Suppose you do have an isolation transformer on the output. Would you |> design |> it so that the secondary winding has a ground tap in the middle, or not? | | No. I don't connect a load to ground so if I had a tranformer on the | output, I would tie one line to ground. This keeps any leakage current from | my load on the output side of the transformer.

And how is a UPS different?

| I think part of your problem is you keep thinking of UPS in terms of | transformers (phase angles between 120 l-g connections to get 208 or 240). | Power electronic devices to not have to work like transformers. Once you | have a DC bus you can do any thing you want.

I'm talking about the "dual conversion continuous online" type of UPS, the only type I ever consider using. It takes the AC input and converts it to DC. That DC is paralleled with the battery with some circuit that manages the usage in some way depending on how sophisticated that UPS design is. Then the DC feeds one or more inverters.

So I have a DC bus. I can do anything I want?

A bypass switch can be present, but some models omit this. I did see a UPS somewhere online once (a rather large one) that had 480V three phase in and 208Y/120V three phase out. I'd say a bypass on that would not be a very good idea. And is it a separately derived system or not?

I see nothing in the NEC that says the inverter is not a separately derived system. A UPS can create a different kind of system than its input. This is easily done when using separate component. It could be done as a whole UPS unit if there was a market demand for it (if it is done anywhere, it is almost certainly a special case). Actually, I did see one once that input three phase and output only single phase (but the loading was balanced on the three input phases, presumably with very near unity power factor).

Looking at just single phase to keep it simple:

A UPS system that has two inverters with synchronized waveforms could be connected as follows:

___Ground / *--[Inv1]--*--[Inv2]--* | | A B

There is no neutral, in or out. The source system may or may not have a neutral. If it has one, it is not used and not connected to.

The bypass switch, if present, is an open transition two pole device.

Where is the short circuit fault? I don't see one. Is there any load current on the ground wire? I don't see where.

You could replace Inv1 and Inv2 with two windings from a single phase transformer. How is this different? Or are you one of those people that always leaves transformer secondaries ungrounded?

But, just for fun, I'll add a transformer to the output:

Ground | *--[Inv1]--*--[Inv2]--* | | \ | | | -------- | ---* A B | | | | *---/\/\/\/\/\/\/\/---* | *---/\/\/\/\/\/\/\/---* | =================== | *--/\/\/\/--*--/\/\/\/--* | | \ | | | --------- | --* | | A B

That's a common 480/240 to 240/120 transformer wired with the 240 windings in parallel and the 120 windings in series so it's a 240 to 240 transformer.

In what way are these two systems different while the bypass switch is in the "not bypassed" position?

Of course if the load needs a neutral or any 120V loading, we can't use this scheme for that load because we can't have load current on the ground wire, on either side. But you could supply a neutral to the output system as a separate wire. That's commonly done on the transformer. I see no reason it can't be done on the UPS other than the fact that you cannot do a bypass on such a UPS because there is no neutral coming in.

For 208V output, the UPS can "bend" the inverters and run them at 120 degree phase angle difference. The inverters will need to handle the effective power factor they will get from that. Add a third inverter and you can do three phase delta in, wye-like out that can serve delta loads (a mix of single phase line to line loads).

Reply to
phil-news-nospam

It definitely looks like all the APC branded 208V UPSes use a floating ungrounded single inverter output. Every model that is designed to also have 120V output uses a step-down transformer to obtain that. And I would imagine that's just one ended 120V rather than 120/240 (which means 2 wire at twice the current instead of 3 wire).

Do their 120V UPSes also work ungrounded? A 120V circuit would have a wire that is designated to be the grounded conductor, so I would think they would have to.

Reply to
phil-news-nospam

| The UPS passes ground straight through. You cannot tie a "line" to ground, | it will create a fault. Therefore it is not separately derived. You can | try, but I would video tape it as it will be fun to watch after.

[...]

| The ground goes straight through the UPS.

[...]

| No. I don't connect a load to ground so if I had a tranformer on the | output, I would tie one line to ground. This keeps any leakage current from | my load on the output side of the transformer.

[...]

| I think part of your problem is you keep thinking of UPS in terms of | transformers (phase angles between 120 l-g connections to get 208 or 240). | Power electronic devices to not have to work like transformers. Once you | have a DC bus you can do any thing you want.

A sales engineer suggested the following unit to me:

formatting link
Maybe you can tell me if this one has a 120 degree "bent" 120/208 output on either 2W+G or 3W+G, as measured by a voltmeter using the EGC as a reference (in case there is no output neutral, which I don't need, since I will be using the 208 volts directly, but want voltage stability relative to ground as part of that). I can take a 104/208 volt "straight" split single phase system, too. Or I can take 120/240. It's all going into a computer power supply that can take 100-240, but I want to limit the current (there will be a lot of these).