On Tue, 25 May 2004 08:31:02 -0400 User 1.nospam wrote: | I saw a new one (to me) yesterday. Trouble shooting an aircompressor | control panel I got strange readings on the incoming line to ground. I had | thought it was a standard 480Y277 service. On one leg to ground I got | 242volts.
And what were the others? 242 and 419?
| I thought I was familiar with all the different configs available in the US, | so imagine my surprise when I examined the three xfmrs on the pole and | discovered that they were connected 480 delta and that one of them had a | center tap, which created a neutral, hence the 242 volts. The connections | could have easily been for 240, 4 wire, which is fairly common here, but it | is definitely 480-4wire. The installation is about 10 years old.
If all you need is 480 delta, then technically you could do it any of 3 basic ways:
- Wye (minimum line to ground voltage of 277 volts each)
- Delta, corner grounded (maximum line to ground voltage of 480 on 2 lines)
- Delta, center tapped (compromise line to ground voltage, 2x240 and 416).
The real question is where/how the neutral line is connected for any power conducting purposes. If it is used, that could dictate the configuration. But if all you have is a grounding conductor for the 4th, then it would not really matter.
| I have done electrical work in this area (Kentucky) for 30+ years and this | is a first. So I ask, anyone else ever seen this? What applications does | it have? Is it common anywhere?
I have seen references to it in some other places, as well as a version of it with 600 volt delta in Canada (2x300 and 520 line to ground).
| Maybe the power company ordered the wrong xfmrs, or got a real deal on a | closeout!
Any answer is possible. It could also have been that they also wanted some
240 volt power somewhere, if not now, maybe back in time. I've looked at a lot of tarrifs and service guides for a number of power companies, and this configuration has in fact shown up in at least one; I remember having seen it there, along with some others like 240Y/139 (most 240 delta loads can use this power and get minimal line to ground voltage) and 416Y/240 (compatible with military generators and some imported three phase equipment). And I have seen 480/240 volt secondary transformers on power equipment catalogs.