| You're right on the voltage drop. I assumed | the string was like the "drawing" below with 100 | feet total wire and 50 feet total length: | | AC --b---b---b---b---b---+ | | | AC ----b---b---b---b---b-+ | | Your voltage drop is based on 200 feet total wire, 100 | feet total length. That's what is shown on the link | he posted, so my assumption was wrong.
If what you show with a "-" is a _single_ wire, then you have wired the bulbs in series, in which case voltage drop will be uniform and not be an issue. But I believe C-9's are all supply voltage bulbs and as such would be wired in parallel. All that I have ever seen are.
If what you show with a "-" is a a _pair_ of wires, then this looks like one of those British ring circuits.
Maybe you meant:
/-+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+- / | | | | | | | | | | | | | | | | | | | | AC O O O O O O O O O O O O O O O O O O O O \ | | | | | | | | | | | | | | | | | | | | \-+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+-
There would certainly be _some_ voltage drop on the latter bulbs and even more if the strings are wired one following the other into the outlet many have on the far end of the plug.
If you were making a _permanent_ installation, such as a series of lamp posts running down a long driveway or road, where the variation in brightness might be detected or even be annoying, then there is this approach for voltage drop uniformity:
/----------------------------------------------------------+ / | / +--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+ AC | | | | | | | | | | | | | | | | | | | | \ O O O O O O O O O O O O O O O O O O O O \ | | | | | | | | | | | | | | | | | | | | \-+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+--+
This could be done with "220 cable" by using the red wire to feed the far end's black wire and leaving the black wire capped off at the close end.
Unfortunately this is not an option for Christmas tree light strings after manufacturing. If someone did make a very long string of say 250 bulbs at
250 feet where this approach might help, not only would it cost more for the extra wire, but might not get a UL listing because it's "strange".