Can anyone explain what the advantages are to having a 460v/3 phase over 208-230v compressor. This is in reference to air conditioning
equipment and I'm trying to determine why you would want a 460v unit over 208-230v or 277v unit. Thanks in advance.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Feb 8, 5:52am, c snipped-for-privacy@yahoo.com wrote:

At 460 volts the current is less for the same power. Example: A 10 hp 208v 3-phase squirrel cage motor with FLA = 30.8 amperes requires No. 8 conductors while a the same motor at 460 volts ahs with FLA=14 amperes that requires No. 14 conductors using 90 degree C copper conductors on a 75 degree termination. Try my calculator at: http://www.electrician2.com/calculators/motor_ver_1.html The disadvantage is 460 volts is more dangerous to work around is less commonly available especially for residential services.