3ph,415v,50HZ motor operate with inveter drive.for instance if the motor is oprate with 25HZ what will be the terminal voltage in the motor.
1.if it is 415? is it possible to oprate with Low frequency.
if it is not what will be the terminal voltage ?how?
regards
T.Venugopal
Didn't find your answer? Ask the community — no account required.
G
Gerald Newton
You need to talk to Rockwell Automation Allen Bradley. They design and build these things. Try:
formatting link
B
Bob Eld
In order to keep the volt-time product constant, the RMS voltage would be
208 volts. This is usually produced by high frequency PWM switching. The operating maximum flux density in the motor is the time integral of voltage. If the time doubles, the voltage halves for constant max flux.
Without this arrangement to control the voltage applied by the inverter, the volt-time product would increase as the frequency lowered .This would cause higher and higher flux density and the motor would draw more and more current until something blew as the core saturated. Bad news!