Current in 3-phase Secondary side of transformer

Hi there all, I was wondering... I have a 3 phase transformer and I'm trying to find the current on the secondary winding.
My transformer is 415 primary 50Hz - 208 Secondary 50Hz
I have the current/power values for my primary winding.
Is there any way that I can find the current/power in my secondary winding?
Is it: Is=Ep*Ip/Es ???
Thanks for your help... PS: If you need any more info, give me a shout.
Shay
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 7/13/06 8:18 AM, in article snipped-for-privacy@m79g2000cwm.googlegroups.com, "shay"

I think you have it right IF your are talking the same winding configuration on primary and secondary. That is Y-Y or delta-delta. Remember that the power going into a leg of the transformer is the same as that going out. Your Es*Is=Ep*Ip.
Bill -- Ferme le Bush
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

---------- Salmon egg has it right but it would be easier if you gave all the data at the beginning. it appears that the transformer may be 415/208 line to line and 240/120 line to neutral Y-Y possibly an autotransformer.
--

Don Kelly snipped-for-privacy@shawcross.ca
remove the X to answer
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Don Kelly wrote:

Hi there Guys, I'll give you a bit more info.
I have recently started a job in a large manufacturing plant in the UK.
This plant has alot of American equipment/machines so voltages are converted to 110 and 208v.
The plant has been having problems as previously there was no standards or conditions for electrical loading on Distribution boards, eg. many board were overloaded and many had very little loading... Therefore leading to some transformers being close to their load limit.
I have recently carried out a survey on the distribution system and have recomended changes, eg cables moved from heavey loaded DB's to light loaded DB's.. this has been actioned and all seems ok... the loads are now shared.
Within the plant there is a computer system monitioring the kW in various boards, these are fed to a PC where loading can be checked etc.
5 of these readings come from 208v circuits.. eg to find the loading on the transformers on the 208 circuits.
The problem I have is that when being installed in 1993 the contractor then installed the CT's on the primary side of the transformer, eg 415v rater than the secondary (i think they were cutting corners). So now... when I get the reading I am getting the reading (kW) from the primary side 415v and not the secondary 208v. This is not giving me the correct reading as this is taking into consideration the transformer power... I just want to see the power/current in my 208 side.
Here's the data I have from the plate on the transformer: The transformer is: ABB Trafo-BB, Type DZV 500kVA V= 433/216 If.7/1336.5 Vector=Yy0 Impedance 3.7%
Here's the reading i've takin for one of the transformers: The line current is: 762A The voltage is: 208v so therfore the kW is: 247kW
These are manual readings... but the reading on the PC which is coming from the Primary 415v side is 324kW. *Note... these are approx values since its such a big num and from different sources so any calculations will not be exact*
Its nearly impossible for me to install 110v or 208v CT's as the equipment must be shut down. Does anyone have any ideas how Is there any way I can get around this... all I'm looking for is the current or power on the secondary side. Thanks loads, Shay
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I guess the decimal points are not at correct places - should be "If7/1336.5A"

762A*208V*sqrt(3)'4kW
The difference between 324 and 274 is 15%

The current at low voltage side in your case should be 2 times less than on primary:
P(high voltage)C3V*sqrt(3)*Current(high voltage)*(power factor) P(low voltage)!6V*sqrt(3)*Current(low voltage)*(power factor)
If we neglect the losses in the transformer - then P(hv)=P(lv), so Current(lv)/Current(hv)C3/216=2 => Current(lv)=2*current(hv)
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 7/14/06 10:36 AM, in article snipped-for-privacy@h48g2000cwc.googlegroups.com, "bobc"

I hate such expressions. What would "one time less" mean? -- Ferme le Bush
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Salmon Egg написа:

I guess it should mean "exactly the same" :-) However, English is not my native language, so maybe I used the phrase improperly - sorry for that.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 7/15/06 12:53 AM, in article snipped-for-privacy@p79g2000cwp.googlegroups.com, "bobc"

I think it was misused EXACTLY as it is misused by many Americans. Sometimes people learning English should not emulate the people they learn from.