| I had a question and I thought that this would be the best place to | search for an answer. I got into a discussion with a fellow engineer | about voltages and efficiency. His claim was that operating equipment | at 480 volt would save considerable energy as compaired to 208 volts | or something simmilar. I understand the savings during the | construction and installation..... smaller wire size, fuses | disconnects and so on, but I told him that you pay for power in kW and | not amps, so there should be little difference. | | I also understand that there is power loss through transformers when | you do voltage reductions, however, I didnt think there was a | substantial savings by operating equipment at 480 volts as compaired | to 208 volts.
Just to make it work out simpler, I'll change the comparison to single phase 240 volt vs. 480 volt. Suppose you have a water heater that has
2 elements designed for 240 volts. You can wire them in series at 480 or you can wire them in parallel at 240. Or you can wire them separate at 240 volts each.
If you have them wired separate and switch to wired in parallel, you basically would parallel the wires, or double the cross section, to handle the capacity.
Now consider going from the wired separate to the wired in series. If the power is a split single phase 240/480 system (240-0-240), and if the two separate circuits are on opposite phase, you can connect the two neutrals together at the heaters. Now you have THE SAME CURRENT as before running in the hot wires, but now there is NO CURRENT in the two neutral wires. So the neutral wires are not longer heating up, and no longer contributing to the losses and voltage drop.
It basically comes down to the fact that losses and voltage drop are in proportion to the SQUARE of the current times the resistance. So if you go from 40 amps at 240 volts, to 20 amps at 480 volts, and use wire that has half the cross section (thus doubling its resistance) the losses are you have 1/4 the loss attributed to 1/2 the current, offset by 2 times the loss attributed to resistance, with a net change of 1/2 the loss. So the higher the voltage, the lower the loss, even though you are using smaller wire.
Back to 480 and 208 volts for three phase (277 and 120 between hot and ground). That ratio is even greater at 2.3094. So if your wire has only 1/2.3094 (0.433) the cross sectional area when you switch to 480, you still have 1/2.3094 of the loss, because 1/2.3094 of the current means 1/5.3333 (0.1875) of the loss on the same size wire (and back to
1/2.3094 of the loss on 1/2.3094 size wire).
So are you ready to convert your home to 480Y/277, yet? I have been for a long time (but 277 volt incandescent light bulbs are expensive and there are code issues to deal with).