I recently posted this to an electricians' forum, it currently has 158 views: but no takers
A problem easily repaired today is much more difficult to explain what occurred because of it. We recently relocated a machine that included a 70 KVA Autotransformer & a primary disconnect. The call-back was not due to problems running: But because when they switched off the X-former's disconnect, it tripped out the overhead bus-duct, (ground-fault!, at the switchgear). I found that the X-former's secondary neutral was landed on machine ground, (a ground wire from the X-former had fallen out of sight in the conduit to the machine). Though the white tape should have caused further investigation, the electrician's oversight was still understandable since:..
1) the neutral lug on the machine was obviously not used,.. 2) both would have a common point in a normal X-former. After connecting properly & allowing production to resume... My challenge is why did the bus fault out while disconnecting?I would love to hear other theories before I divulge mine.
Hint: my explanation involves the electrics of a classic car!