my original message;
>> I recently posted this to an electricians' forum, it currently has 158
>> views: but no takers
>>
>> A problem easily repaired today is much more difficult to explain what
>> occurred because of it. We recently relocated a machine that included a >> 70
>> KVA Autotransformer & a primary disconnect.
>> The call-back was not due to problems running: But because when they
>> switched off the X-former's disconnect, it tripped out the overhead
>> bus-duct, (ground-fault!, at the switchgear).
>> I found that the X-former's secondary neutral was landed on machine > ground,
>> (a ground wire from the X-former had fallen out of sight in the conduit >> to
>> the machine).
>> Though the white tape should have caused further investigation, the
>> electrician's oversight was still understandable since:..
>> 1) the neutral lug on the machine was obviously not used,..
>> 2) both would have a common point in a normal X-former.
>> After connecting properly & allowing production to resume...
>> My challenge is why did the bus fault out while disconnecting? >>
The transformer as shown is not an autotransformer but appears to be ( hard to tell from the diagram except that there is primary/secondary isolation and no neutral on the primary) a delta star 2-winding transformer. Please clarify this. Autotransformers do not provide isolation but have part of the winding common to both sides. Please check the wiring diagram. I have a suspicion with regard to what is happening -if it is a true autotransformer- but the diagram doesn't provide such information.