I have a 400v 5.5kW 4 pole motor driven via a frequency inverter at 50Hz. If I increase the frequenecy to 60Hz, the rpm will increase but
how much more power (kW0 will the motor draw?? Is is just another 20% reflecting the 20% increase in frequency??
TVMIA
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 11/18/07 12:07 PM, in article snipped-for-privacy@b15g2000hsa.googlegroups.com, "CS"

It is not a simple question. The answer will depend more on the torque-speed characteristics of the load than anything else. Less magnetizing current will be drawn. Depending on how the motor was designed, the magnetic losses can be higher or lower.