The water association I am with had contractors install a 240 volt, three phase, 10 H.P. submersible pump for our community water system. After connecting it to a VFD, THD measurements on the three legs, with the pump OFF, were 93.5%, 84%, and 90.4%. With the pump ON, the THD measurement on leg 1 was 23.2%, (with no data recorded for the other two legs, sorry). Line voltages were 209, 209, and 211 V.A.C.
The pump has been operating since May 6, 2007, maintaining water pressure between 40 and 60 psi as designed, ramping up and down properly, with no apparent problems.
After reading about THD, I am concerned about the long term effects the THD might have on the motor. Also, could someone comment about the THD values that were recorded (they seem extremely high when the motor was off, and above standards when the motor was on).
FYI, there is a school building connected to the same transformers that are providing power to our pump. To my knowledge, there are no VFDs at the school or any devices that would cause the THD percentages to be so high when our pump is off. The school does receive three phase power to drive A.C. motors for 1-3 H.P. ventilation fans and water pumps using simple on-off relays.
So far, the engineers behind this project have been silent, so I am trying to increase my understanding about THD problems.