How do I connect PTs and CTs for 400A 3ph service

| Actually, quite often an in-line resistor/shunt is *not* safer. If the | primary circuit is high-voltage, the leads used to sense the voltage drop | across the shunt will also be at line voltage. One of the advantages of | CT's is the secondary circuit is *low* voltage ( My question was one of practices ... a politics category. And apparently |> one that some engineers want to keep others from learning about ... | perhaps |> to protect their jobs. | | Occam's razor. Don't assume nasty conspiracies when the simpler answer is | you just haven't made your question clear enough for people to understand.

That could be. Too often people are put off be highly detailed, precisely expressed questions (they get tire of reading it after 100 words or so). So I more often try to be brief ... too brief in some situations.

| You don't. You have to make the initial installation with the system dead. | As part of the initial checkout, you verify the shorting links work | correctly. If you have to work on the metering, you either kill the | circuits, or trust that the shorting links still work correctly. If you | have any doubt about the shorting links, you don't trust them and have to | reschedule the work when the system is dead.

My trust in technology is limited when it can kill. Things break. Things come loose. Things don't have expected capacity, etc.

| If the shorting links are separate from the meter and normally open, you | should see the meter reading drop to near zero when the links are closed. | If the reading doesn't change, then obviously the link isn't shunting | current away from the meter. Some meter cases have 'finger blades' that you | pull to disconnect the meter and short leads at the same time. So when you | pull the 'blade', the meter goes to zero, even if the shorting fingers fail. | These types of cases have been around since Westinghouse, shorting-link | failures are very rare in this type of unit (after all, it isn't rocket | science, they designs are simple and robust).

Still, a failure can kill. I think we can accept that technology is not 100% perfect. Goals are in terms of MTBF and percentages, etc. Life is just once.

| Some CT's have a thin (mica?) member between the secondary terminals. If | inadvertantly open-circuited while energized, the voltage spike will | 'puncture' the insulation member and allow an arc to jump across the | terminals right at the CT. Have to replace the CT to repair it, but the | high voltage won't be sent through metering lead damaging other components | (or people). Not *all* have this feature.

Sounds like a good idea.

Reply to
phil-news-nospam
Loading thread data ...

On Sat, 14 Feb 2004 10:17:08 -0500 BFoelsch wrote: | If you are truly worried about it, you disconnect the load from the shorting | bar, check it with a meter, reconnect it and remove the short!

If I'm going to do that, I might as well de-energize the whole thing, and remove the short before re-energizing.

| CTs and shorting bars are used safely everyday, everywhere. A CT is NOT | going to set fire to the curtains in a millisecond, it just can't deliver | that much power. It can produce hazardously high voltages, but not at high | currents. Take a look at the saturation curves of some CTs for a real | education. In practice, you start to loosen the shorting strap, and if you | see or hear arcing, you tighten it back up!

Something that can't deliver more than 1 ma at expected current draw might be safer to handle. Fire isn't my first worry, though it is certainly a valid one.

| For your application you should perhaps investigate current transducers | rather than CTs. Small, Hall effect devices that typically have better | frequency response than CTs and eliminate this whole (non)issue of secondary | voltage.

Any particular good keywords to google for to find these?

| I find it kind of amazing that you are designing a product like this from | scratch; there are any number of UL listed assemblies available with all | kinds of network connectivity. Check out the offerings by Allen-Bradley | (PowerMonitor)and Square D (PowerLogic). I would bet that either of these | would do everything you need and more.

I've seen some around, but none have a usable output interface. The output but be optically isolated no matter what method of measurement is used, and a standard and/or documented data path and format (no proprietary software). One I did look at simply provided minute by minute watt/hour usage, which is way off from what I'm doing. Another seemed like it might have more data being handled, but required the use of their software (for Windows, which immediately rules it out), which negates the flexibility of designing my own logic.

Reply to
phil-news-nospam

formatting link
is a starting point for not too stringent requirements.

Reply to
BFoelsch

|> | For your application you should perhaps investigate current transducers |> | rather than CTs. Small, Hall effect devices that typically have better |> | frequency response than CTs and eliminate this whole (non)issue of | secondary |> | voltage. |>

|> Any particular good keywords to google for to find these? | |

formatting link
is a starting point for not too stringent requirements.

It appears they only sell the raw sensors in large bulk. Maybe Digikey has them in single quantities.

Reply to
phil-news-nospam

It might be helpful if you told us what you are trying to do, not how you want to do it. So far you have not mentioned what you want to accomplish. You have posted how you plan to do it (isolated input to a computer, sampling rate, etc).

If we know what you are trying to accomplish we may know of instruments that can provide what you need without the need for all of the custom work that you are proposing.

If it has to do with harmonics monitoring and or harmonics compliance, there are many products available.

Just a thought.

Charles Perry P.E.

Reply to
Charles Perry

| It might be helpful if you told us what you are trying to do, not how you | want to do it. So far you have not mentioned what you want to accomplish. | You have posted how you plan to do it (isolated input to a computer, | sampling rate, etc). | | If we know what you are trying to accomplish we may know of instruments that | can provide what you need without the need for all of the custom work that | you are proposing. | | If it has to do with harmonics monitoring and or harmonics compliance, there | are many products available.

I want to get the voltage and current waveforms into a Linux based computer for the purpose of processing it in ways that I want to be able to program. The software I will write will be analyzing the data for things that I want to be able to customize without having to know them all today. At first it may be to simply measure load usage. But then I will add on other analysis, including harmonic, reactive, noise, RF, BPL, and then perform logging and remote control of devices.

My objective isn't to do a specific analysis, but rather, it is to make this data an input so I can explore what analysis and controls I can do. Once the data is in the computer in real time, then it has moved from a realm I am not an expert in (hardware) to one that I am an expert in (software).

I want to keep the hardware minimal, though I also want to protect computer hardware from added risk of any new connection to power. The computer _may_ even run entirely isolated, using a battery, or if not that certainly a UPS.

I'm not interesting in buying an instrument that does the analysis for me, nor am I interested in using someone else's software that does the analysis (although if it an open source version, I may be curious to look at it to get ideas).

Right now my first thought is to feed an analog waveform into a sound card and explore from that. Eventually I see doing multiple channels of data in digital form (still to be decided), and multiple channels of device control.

One long term objective is to manage load from selective devices based on the level of other uncontrolled loads. If other loads are low, more of the managed devices can be on at the same time. If other loads are high, fewer of the managed devices can be on at the same time. That objective would be to maintain a controlled peak load, especially when the power source is not from the power company.

But that's not the only objective; it's just an example. I won't even be able to envision all the possibilities until I get started and see how much data I really get and what I can analyze from it.

So basically, the first objective is to just get the data into the computer.

Reply to
phil-news-nospam