How much starting and stopping of ac motor is acceptable?

I have fan ( 1/3 hp 3 ph 460 vac) for a fluid cooler which repeatedly cycles on 1 minute and then off 1 minute. I am afraid it might run hot and burn out prematurely. How can I determine a safe cycle period and duty cycle for this motor? Do I need more info than is available from its name plate? Thanks, Dave Miller dvm001atrochester.rr.com

Reply to
D.Miller
Loading thread data ...

in article 0DFTb.20115$ snipped-for-privacy@twister.nyroc.rr.com, D.Miller at snipped-for-privacy@rochester.rr.com wrote on 2/2/04 8:40 PM:

My guess is that you are ok. You do not describe the motor well. I presume that it is an induction motor. I also presume there are no tricky starting sequences.

Except for starting transients and power factor, just monitoring the temperature of the windings to make sure you do not overheat them should be enough.

Bill

Reply to
Repeating Rifle

Thirty starts an hour seems to be rather a lot. You're unlikely to be able to adequately instrument the motor for temperature rise to confidently know whether this number of starts is acceptable. Generally 6-8 starts an hour is acceptable but 5 times that rate should get some advice from the motor manufacturer to see what the motor is actually designed to take.

Reply to
Miles

Some center pivot irrigation motors operate on a one minute cycle. They start and stop once per minute. Some others run on a 30 second cycle so they start and stop twice a minute. The pivots in the U.S. operate on 3ø

480VAC and the motors last for years. The motors are rated for continuous duty.

Dean

Reply to
Dean Hoffman

You need to know 2 things; the motor speed (actually the number of poles, but speed will tell you that) and the intertia of the load.

There is actually a formula for this. NEMA publishes a chart for motor duty cycle design. The determination is the LESSER of the following 2 choices, assuming that it is a 4 pole (1800rpm) motor design, A) 38 starts per hour. This is essentially an UNCOUPLED rating B) 5.8 starts per hour x Wk2 (the load inertia)

If you do not know the load inertia value it is NOT safe to assume that 38 starts per hour is OK. I.e. if the Wk2 is 2.5, the calculation for method B is 2.5 x 5.8 = 14.5 starts per hour. So if you do not know the load inertia, you can't safely answer that question.

BTW, In either case, the MINIMUM rest time between starts is 38 seconds on 4 pole motors up to 1 HP. If it is a 2 pole (3600rpm) motor, that goes up to 75 seconds, a violation of design criterea for your application right there.

Reply to
Bob

It must be a 6 pole motor as rpms are approx 1200. The unit is sealed under a sheet metal hood which makes it difficult to access the motor name plate info. As a result I don't have a manufacturer or model number available. I am speaking with the vendor who sold us the unit. I would much rather speak directly with the motor manufacturer. There is a lesson here... and that is to document name plate info on all equipment we receive.

I can increase the cycle period by getting a new thermostat with an adjustable differential. Instead of a 4°F differential I can probably live with an 8°F one. Ultimately I would like to get a firm answer from motor manufacturer.

I thank everyone for their comments.