How to meassure the pressure different of different environment.

Oct 27, 2003 12 Replies

First reply

John Gilmer

With a manometer. You can buy a sensitive differential pressure guage that will do the same thing. In those circumstances, pressures are measured in INCHES of WATER. SO: if you want to go the DYI route you pick a location where you want to monitor the pressure and you bring…

Read the full reply

Our company intend to build a clean room with possitive pressure in the room.We will install a blowing fan to suck the air from outside into the clean room with the damper control.



Can anyone know how to meassure the pressure different between inside and outside of the clean room.



Thanks



Vincent


With a manometer.

You can buy a sensitive differential pressure guage that will do the same thing.

In those circumstances, pressures are measured in INCHES of WATER.

SO: if you want to go the DYI route you pick a location where you want to monitor the pressure and you bring tubes from INSIDE the enclosure and OUTSIDE the enclosure. You connect these tubes to a U shaped glass or plastic (transparent) section of tube with arms on the order of 10 to 18". Before connection you put some WATER in the tubes to fill each arm about 5". When you complete the connection the DIFFERENCE between the water level in each side of the "U" is the pressure inside your room.

You can buy "scientific" versions of the above thay feature a large (very) diameter tube on one side and a sloping tube on the other side. For pressure differences of a fraction of an inch, the sloping tube permits a more accurate measurement.

But, basically, all you need is some clear tubing, a ruler, and some water.

  1. If all you want to do is be able to monitor the pressure difference: search "differential pressure gauge" at
    formatting link
    . There's zillions of varieties and prices.
  2. If you want to actually maintain (control) the pressure difference by varying the damper postion you could use a differential pressure transducer or transmitter as input to a PID controller. The output of the controller would then control a proportional damper actuator. Or you could keep the damper stationary and use the differential pressure transducer as input to a Variable Frequency Drive (VFD) to control the blower motor speed (assuming you have a three phase power system). Many standard VFDs have built in PID control functionality so you wouldn't need any other control devices but the transducer and the drive.

formatting link
probably has whatever gauge, transducer, PID controller (no VFDs), etc. you would need.

Perion

I believe a magnahelic gauge is used.....the last one I purchased was from graingers for about 50 bucks...

If you do opt to make your own water gauge, consider adding a little soap to the water: surface tension effects can cause small errors.

And a drop of food coloring can make it easier to read against a ruler background ;-)

daestrom

You've received some good answers to your question, but no one has suggested that you will need to filter the incoming air. Although I hope you've already taken that into consideration, outside air only appears"clean". Check the outside air filters (if you have them) on your HVAC units for a good example of what is in the air you intend to put into this clean room, and that's only the big stuff! Depending on your process, material you can't readily see with the naked eye will contaminate the area.

Without specifying your application one can only guess as to the need for climate control (heat, and humidity, etc.), and the need to disconnect any normal HVAC units now serving the area (this will affect the pressure gradient measurements, and introduce contaminates).

Louis--

********************************************* Remove the two fish in address to respond

for what it's worth, I have a couple of magnahelic gauges for $15 each - if interested, contact me off the list at william_b_noble at msn dot com

I also have this cool purge control panel that has a magnehelic gauge and a bunch of other goodies up for auction on E-bay.

bill

Along with the pressure you need to monitor the humidity as well, since humidity is a factor in air density.

You monitor humidity if the process requires a certain range of humidity.

Your basic clean room is pressurized so that "leaks" take conditioned air out and un-conditioned air doesn't come in. The "conditioned" make up air would have to have moisture added or taken out as required by the process.

It sounds to me like the slack tube manometer may be the easiest solution with the magnehelic guage being the most elegant. One thing with slack tubes, the water evaporates pretty fast so you probably want a more stable operating fluid. You can calibrate your "ruler" to anything from mercury to motor oil.

Since oil is lighter than water, the oil gauge will be more sensitive.

True. Have made them using a 'pinch' in the ends to help this. And adding a small amount of oil on the water surface (be sure to add the same 'thickness' to both sides) will make the water last a long time. Have seen some using a red oil that also makes reading against the scale easier.

daestrom

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required