What seems to be the consensus regarding mixing general purpose receptacles with general lighing? I like to mix, partly for load diversity, and partly because I wouldn't want
a whole bunch of lights to turn off if one cct is being worked on.
So what do you prefer? reasons?
Romy
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
The homeowner would like several circuits in every room so a tripped breaker would not make the whol room dead but fiscal reality severely limits that. I wire the walls on one circuit and the ceiling fixtures on another. I suspect the AFCI requirement has made every bedroom outlet in the house on one breaker if they can get away with it. From a strict "hold your nose" interpretation of the code, you can put 800 square feet of bedroom on one 20a AFCI.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

breaker
suspect
breaker
A typical house that I'd wire generally has 2-3 AFCI breakers, spread across 3-4 bedrooms. I usually limit most cct's to 8-10 devices just for the heck of it. On the AFCI topic, is bedroom lighting normally put on ccts protected by AFCI's?

It always sounds so strange when I hear "20A" cct. Until recently (kitchen 20A GFI requirement), 20A cct's were never really used here (Canada) in residential applications. The U.S. must have many more uses for it.
Romy
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
A responsible builder will probably use one AFCI per bedroom but I would still think you should split up the loads a little. Since the 2002 code all outlets in the bedroom, including the lights, shall be AFCI. (US) We are finding that some ceiling fan controllers are tripping AFCIs.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
I do not understand why you insist on 1 circuit per bedroom, there is actualy very litle load in typical bedroom. Home owner hes to pay for the "extras". As to the separating the lighting circuits and plugs, it has few adventages I can see: 1) for economical reasons - you can put more then 12 lights on one cct because the maximum load is known, 2) you can turn on fairly safely the lighting circuit to provide the light for the painters and others before the final inspection, 3) one timer and one photocell can easily make you house "alive" when you go on extended vacations ;-), 4) truble finding might be easier due to more structured approach. So far I was mixing the lighting circuits and plugs, right now I am co-managing the construction of my own house (lot of fun), I will give it a try and separate the lightin and receptacles. Art.

still
shall be

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
In article

Can't speak for the NEC but;
It is not commonly done at final circuit level but in commercial installations it is frequently done at distribution board level.
In the UK there is an obligation (can't remeber BS7671 or elsewhere) to minimise the disturbance caused by a circuit trip. You would have to spur off a socket outlet with a fused spur for any lights on a socket circuit. The practical upshot of this is a socket circuit for kitchen and one for other rooms and a separate circuit for upstairs and downstairs lighting. Considering the low cost of circuit breakers and cable and the faffing about with spurs it is easier just to keep lighting and sockets separate. Most installations run for years without breakers tripping.
--
Z