On Mon, 09 Oct 2006 02:24:05 -0500 Bud-- wrote: | snipped-for-privacy@aol.com wrote: |> On 8 Oct 2006 17:52:49 GMT, snipped-for-privacy@ipal.net wrote: |> |> |>> I'd bet the UL rules are based on the box size, and with |>>the right space,more slots would be OK. What we probably have to wait |>>for is the formalized testing of the new larger boxes. |> |> U/L will do whatever the manufacurer's tell them to do. |> They manufacturer can submit a 200 slot panel and U/L will test it and |> if it doesn't burst into flames they will list it. |> Whether an AHJ actually accepts it is up to the AHJ as guided by NFPA, |> NEMA or their local union rep. | | The NEC currently allows single phase residential panels with 42 poles. | Does anyone make a 100A panel that allows installation of more than 20 | poles? Or more than 40 poles in a 200A panel? Far as I know the UL | standard does not permit it.
Eaton Cutler-Hammer has listed in their catalog, CH series panels that have up to 30 spaces for 100 or 125 amp, 32 spaces for 150 amp, 42 spaces for 200, 225, 300, or 400 amp. These are main breaker panels. Main lug panels only go up to 24 spaces for 125 amp, 32 spaces for 150 amp, 16 spaces for 200 amp (probably just an odd bus here), and 42 spaces for
225 amp. I suspect some of the lower amperage MCB panels really have larger busses but with mountings for smaller main breakers.
Square-D has similar, but I did notice a 100 amp MCB panel up to 32 spaces in the QO series.
I did not look at BR or HOM series, or other brands like GE or Siemens.
Do you have a copy of the UL standard that limits 200 amp panels to no more than 40 poles?