Hi frnds, m much confused in fundamentals of neutral. I want help of u ppl regarding that. My que is when neutral gets open in distribution network i.e aftr xmer secondary at far end or last leg of the distribution cable .nd distribution network is earth at multiple point with neutral grounded. Then wht will be the phenomena ? Over voltage at consumer load side will happen bt wht exactly happes technicaly that is wht i need. Nd wht are the protection which can help in this case.suggest also a link or site that can give drawing nd calculation 4 that. Urgent pls

Reply to
prady
Loading thread data ...

Be an idea to polish up your english before you worry about electricity.

Whatever you native tongue is, SMS shorthand does not work well for asking technical questions.

-- John G

Reply to
John G

| m much confused in fundamentals of neutral. I want help of u ppl | regarding that. | My que is when neutral gets open in distribution network i.e aftr xmer | secondary at far end or last leg of the distribution cable .nd | distribution network is earth at multiple point with neutral grounded. | Then wht will be the phenomena ? Over voltage at consumer load side | will happen bt wht exactly happes technicaly that is wht i need. Nd wht | are the protection which can help in this case.suggest also a link or | site that can give drawing nd calculation 4 that. Urgent pls

If there is only one hot wire in the circuit, open neutral means the current stops flowing.

If there are two or three hot wires in the circuit, the open neutral is no longer able to balance out the currents and voltages.

Each load or group of loads that are connected to the two or three hot wires would, without the neutral, be operating in series between those hot wires. If the resistances of the loads are equal, then it happens to be in balance and there would not be current on the neutral even if it were not open. But if the resistances are different, then the load with the higher resistance gets a higher voltage because the other load is not resisting enough.

More technical:

There are 2 hot wires, black and red (USA color standards). There is one neutral, white. A 60 watt light bulb is between black and white and gets 120 volts (USA voltage standard). A 15 watt light bulb is between red and white and gets 120 volts in the opposite phase. The resistances of these at operating temperature is 240 ohms for 60 watt and 960 ohms for 15 watt. For the sake of description, I will assume the resistances will remain constant (really, they won't, but they will be somewhat close to the same proportion). There is 0.5 amps of current through the 60 watt bulb and 0.125 amps through the 15 watt bulb.

There is 240 volts between the black wire and red wire.

Now disconnect the neutral. What we have now is two bulbs in series connected to 240 volts. The resistance of both in series is 1200 ohms. At 240 volts that will be 0.2 amps of current through both bulbs. In the bulb with 240 ohms, since 0.2 amps is flowing through, the voltage drop across the bulb is 48 volts. Now it is dissipating a mere 9.6 watts. It would be very dim. The other bulb with 960 ohms also has 0.2 amps of current flowing through it. Both have to have the same current if they are in series. But in this case the voltage drop across 960 ohms for

0.2 amps is 192 volts. And that means the bulb is dissipating 38.4 watts.

The sum of the voltage drops, 48+192, is 240, our supply voltage between the black and red wires.

But the 15 watt bulb is overloaded at 38.4 watts and the 60 watt bulb is underloaded at 9.6 watts. The 15 watt bulb is likely to burn out real soon.

I hope you can see that when you consider various appliances in this kind of situation, when the loads are out of balance, some get more and some get less voltage.

Now consider what if instead of a 15 watt bulb, there were 2 7.5 watt bulbs. Those two would be splitting the 38.4 watts between them at 19.2 watts each. If you saw this kind of thing happening, you might well be tempted to shut off the first overloaded bulb you see. But that would actually be bad for the 2nd overloaded bulb because this makes the out of balance even worse.

If you ever encounter a case where you suspect a broken neutral and there are many appliances on and some are overloaded and some don't have enough voltage (which can even damage them that way, too) ... DO NOT ... DO NOT shut off any appliance individually. Instead, immediately go to the MAIN shutoff switch for the building and shut off ALL the power at the same time. DO NOT shut off individual breakers. ONLY shut off the main breaker. Then call a qualified electrician to diagnose the problem and find where the neutral break is.

Reply to
phil-news-nospam

I guess he's asking about neutral failure in PME/TN-C-S supplies. However, I'm not going to waste my time on a detailed answer when the question was so unintelligible as to be uncertain what's being asked.

Reply to
Andrew Gabriel

The frightening part is some of these guys are going to be preparing reports one day !!