| I understand that there are countries where the primaries of the | distribution transformer are not connected to the ground/earth in any | way (from the perspective of the customers ground). This is not | necessarily a 'better' or safer system. There are complex trade-offs | involved and there are a lot of good reasons (for increased and other | reasons) for making sure that at least one primary lead of that | transformer is earthed.
Being earthed is one thing. Connecting primary and secondary neutrals is another.
| In the USA, there is a special case exception in rural areas where | there are problems with stray voltage traveling through the earth in | farm situations. One solution is to use a special neutral isolator to | keep the secondary neutral/ground/earth disconnected from the primary | ground unless the voltage difference reaches a certain threshold, in | which case the bond is re-established.
So are you saying stray voltage never happens anywhere else by in rural areas? How clever of those electrons to recognize that.
| Not everybody does it that way. France is one such country with the | TT Earthing Scheme. In other words, the power company does not supply | any grounds to the customer on their distribution lines. The customer | is responsible for providing their own local earth connection that is | not connected to the larger distribution network. For safety, an RCD | (Residual Current Device) is required for such installations. An RCD | is similar to what we know in America as a GFI or ground-fault | interrupter. However it is not exactly the same. Typically, an RCD | is set to trip on a ground fault with a greater current than the | typical GFI 5ma threshold and also it contains complex timing circuits | and often covers more than just one circuit.
In many countries, an RCD main is required. I've seen the requirements of such for Japan.
| | In my opinion, the North American scheme gives several advantages when | safety is concerned as you have the following unique features when | compared to the typical Euro Systems that use the RCDs. | | 1. Individual circuits can be protected by inexpensive outlet-type | GFI's or slightly more expensive breaker GFI's. As mentioned | previously, RCD's are expensive and complex. | | 2. Unlike a typical RCD installation, the whole house is not plunged | into darkness should a single GFI trip due to a real fault or from | testing. | | 3. In the North American System, 240 V. is available (via the split | phase wiring scheme) for the larger appliances that need it (range, | dryer, large air conditioner). However, at no point is any voltage | inside the house higher than the nominal 125 volts to ground.
... except when the effects of MV distribution systems are factored in.
| 4. Bathrooms are arguably safer and more convenient to wire | electrically. You don't need to worry about 240V wiring near the sink. | Light switches can be conveniently mounted on the wall (instead of | using pull chains), you don't need to install isolation transformers | as they do in the UK for shavers. Outlets don't need to have switches | on them and because of the lower voltage, you have less paranoia about | bonding everything together in the bathroom. Hair dryers can be | safely plugged into convenient bathroom outlets protected by GFI's, | etc. | | I've seen some of the wiring in France and I'm not sure what they did | before RCD's became widely used. Did they just not care if anything | was grounded? I'll bet it wasn't all that safe. | | I'm old enough to remember the days in the USA (late 1950s and early | 1960s) when we switched to plugs and outlets with 2 prongs to 3 | prongs). The electrical system became a lot safer, as a result, | particularly for users of portable power tools. Double insulated | appliances and the later GFI requirements provided further safety | improvements.
Safer, yes. But I still think the safety can be improved even more by better isolation from the MV distribution.