I have a problem with a circuit in my apartment that continues to go off and the maintenance hasa looked at the circuit and can not figure out why it keeps going off. The circuit breaker doesn't trip off, th ecircuit to the bedroom and bathroom will go off and within minutes, it will come back on by itself. Any suggestions would be acepted...
Most likely a loose connection heating up and it is a serious fire hazard. Most states have laws allowing a renter to fix serious flaws in their dwellings if they are not taken care of by management in a timely manner. I would look into that and stop using it until it is fixed properly.
I have to agree with "Long Ranger". It sounds very much like a loose/intermittent connection. This sort of thing can start a fire if not fixed promptly.
Insist that the landlord bring in a qualified electrician (not his usualy 'handy man') to test the circuit. Show him what you're doing when the circuit acts up.
He did remove the first switch from the electrical panel and found the wires were back stabbed in the switch and removed them and placed them on the screws. This was the first switch serving the rest of the room. When power went off, this light ws one of the lights that was out when it went out... he also relocated the wire from the breaker and placed it on ad different breaker that was serving a different plug.
If he had tightened the connections in the panel and made sure all were tight, then where else would the problem have been that would make the entire circuit do dead?
There could be splices along the circuit, and any one miight be bad. I saw this happen once when a wire nut fell off of a splice behind a receptacle, which intermittently killed power to two rooms that were daisy chained from there.
This is not typical of Federal Pacific breakers. Older ones are notorious for a particular problem, but that involves failure to trip.
Some circuits might be wired so the feeder into an outlet is under one set of screws, and the feeder out under the other set of screws. So if the first outlet has a loose screw, all the outlets downstream are affected.
Worked on one house where the living room outlets were acting up. Checked the service panel and found nothing wrong. But between the living room and service panel, was an *unused* outlet in a bedroom (don't know who wired that place, it was nasty). When we pulled the child-proof safety cap off the outlet (children's bedroom), the plastic prongs that fit into the outlet were all melted/charred. Replaced the outlet, problem solved.
So it can be *any* receptacle or device in the string, not just the one you're plugged in to.
PolyTech Forum website is not affiliated with any of the manufacturers or service providers discussed here.
All logos and trade names are the property of their respective owners.