I am trying to run a 4.5kVA, 240V to 420V step-up transformer from a 240V supply through a C20 MCB; however, the insurge current at switch-on always trips the breaker. I have 6mm sq cable from the consumer unit to transformer. If I reduce the cable to 2.5 mm sq, the system works perfectly, I assume due to the increased reactance of the thinner cable restricting the max current. I would like to retain the larger cable to limit the voltage drop across the system and I am reluctant to increase the size of the breaker, as a 20A breaker should give protection for both the supply cable and transformer (wiring regs suggest a C20 breaker should be able to handle up to 200A for the time period required until the transformer reactance has built up.
Can anyone suggest the correct size of breaker for this installation, or a means of limiting the initial insurge until the transformer field has built up sufficiently to self-limit the current? Once up and running the transformer only draws 1-2 A off-load. Thanks,
Eric