Residential power wiring: mounting electrical box outside?

Need to put an alarm buzzer (outside rated) on an external stucco wall. The buzzer has a 3/4 opening on the back of the 4x4 cast housing for a standard conduit / flex fitting or strain wire clamp / bushing.

Have outdoor (NEMA 3, I think) 6x6x4 box.

Buzzer needs to face away from stucco wall.

So, how best to mount these? If I use NEMA box, cover is on face (away from wall), and I don't think you can mount anything on a cover (inspector might not like that : -). Any other surface faces the buzzer in a direction other than away from the wall.

If I mount the buzzer directly on the wall, this puts the 3/4 hole against the wall. Is it acceptable to put conduit or flex through the wall directly to the back of the buzzer?

Other orientations?

Suggestions welcome.

Thanks,

Reply to
DaveC
Loading thread data ...

stucco wall. The

for a standard

face (away from

(inspector might

direction other

3/4 hole against

the wall directly

Sure, use urethane roof sealant in a calking tube on the back of the box and around the wall penetration... use 3 cement screws to hold the box aganst the wall (drill first) you can also run romex though the wall into yer box if the building is not over 3 stories. you dont need conduit in a wall.

Phil Scott

Reply to
Phil Scott

Why not? they see flood lights and motion detectors in 3R covers every day. Just be sure to get one with a 3/4" threaded entry. Then you just use a close nipple from the electrical department. (plumbing pipe is not buffed out)

Reply to
Greg

On Thu, 14 Oct 2004 17:16:54 -0700, Greg wrote (in article ):

The 3R box I have has no hole. Planned on making my own hole (not threaded). Buzzer has 3/4 hole on back (not threaded). Is it the *threaded* hole that makes this OK?

Can't I just use an electrical close nipple and nut between the two non-threaded 3/4-inch holes? Probably lots of caulk / sealer, too.

Thanks,

Reply to
DaveC

If you are going to do something like this I would suggest securing the buzzer directly to the cover and just using a bushing. If this is just a flat cover, the threads on a bushing should be long enough to go through the cover and still have plenty to get into the buzzer entry threads. I would still use some screws to hold the buzzer to the cover.

Reply to
Greg

On Thu, 14 Oct 2004 20:19:13 -0700, Greg wrote (in article ):

So you would recommend using the NEMA 3 box and not directly mounting the buzzer to the wall?

Can I run conduit or flex or romex directly into the back of the NEMA box from inside the stucco wall? As someone else suggested, using lots of caulk or other sealant between the box and the wall...

Thanks,

Reply to
DaveC

What does the manufacturer suggest?

Maybe I don't understand exactly what you have. If the leads come out of the buzzer you need a place to splice them. I assumed that was why you have a box there.

It happens all the time.

Reply to
Greg

Soffit?

Reply to
Richard J Kinch

On Thu, 14 Oct 2004 15:24:17 -0700, DaveC put forth the notion that...

Sure. As long as it's a weatherproof box, and the buzzer can be removed from the front to allow access to the splices.

Reply to
Checkmate

On Thu, 14 Oct 2004 22:42:35 -0700, Greg wrote (in article ):

Buzzer was old installation, which I am re-configuring (installing new alarm; buzzer was part of old alarm). Don't know mfgr...

Buzzer consists of its own cast box (approx 4x4) w/ 3/4 hole in the back, and cover. Cover consists of square buzzer mechanism ( grille, diaphragm, electro-mech buzzer ), with pigtails. Splice can be made within the buzzer's cast box.

Reply to
DaveC

On Fri, 15 Oct 2004 10:46:28 -0700, Checkmate wrote (in article ):

Thanks,

Reply to
DaveC

On Sat, 16 Oct 2004 09:39:16 -0700, DaveC put forth the notion that...

I've done similar installations where I had a 4S box on the inside of the wall, and a nipple through the wall to the outside box. If you're not going to have anything surface mounted on the inside of the building, you can still use flex or Romex (depending on local codes) and terminate it on the back side of the box with an approved connector. When you screw the box to the wall, slobber some silicone behind it and you'll be fine.

Reply to
Checkmate

PolyTech Forum website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.