We have been using Reliance Flexpak 3000 DC drives to supply the conveyance drives on our machines for about 7 years now and have experienced frequent motor bearing failures due to voltages being induced into the rotor and discharging through the tail bearing. I realize this is a common problem in the drive industry but we also use many other types of drives AC PWM, AC Sensorless Vector Drives, And Minpak DC drives from many other manufacturers including Allen Bradley, Lancer, Toshiba and we have not seen the bearing failures with these other drive systems. Does anyone have any suggestions to prevent these effects and limit the voltages induced. We have run tests by isolating motors and found 70 VAC on the motor casing to ground. In talking with Reliance support they suggested building a filter on the output of the drive to smooth out the waveform but they couldn't spec out capacitor and inductor values because each filter application would be speed, load dependant. Thanks in advance for any help