Neighbor has an underground cable which he wants to splice (to make longer) and throw back into the ground. It's not in conduit and I don't think there's a way to splice it. Am I right? What's the rule?

Reply to
N7RX
Loading thread data ...

There are listed splice kits for buried cables

Reply to
Greg

There are several manufactures that make listed kits for ug. 3M and Raychem come to mind. This might help

formatting link

Reply to
SQLit

There are splice kits sold for this purpose.

Reply to
bob peterson

They make splice kits for direct burial. They have a heat srink insulation.

Reply to
Kilowatt

Cold Shrink splices are easier to use in my opinion. I believe 3M has a line of them.

Charles Perry P.E.

Reply to
Charles Perry

fwiw, there are twist on wire nuts rated for underground use. I watched in amazement when an electrician used them in an outdoor lighting application, where the ground was always wet.

Then there's this: with pumps that are submerged in a well, I had seen underwater electrical connections protected with multiple layers of electrical tape.

Reply to
tony

"N7RX" wrote in message news: snipped-for-privacy@corp.supernews.com...

The NEC requires that wire connectors or splicing means installed on conductors for direct burial shall be listed for such use. Here are some of the rules:

110.14 (B) Splices. Conductors shall be spliced or joined with splicing devices identified for the use or by brazing, welding, or soldering with a fusible metal or alloy. Soldered splices shall first be spliced or joined so as to be mechanically and electrically secure without solder and then be soldered. All splices and joints and the free ends of conductors shall be covered with an insulation equivalent to that of the conductors or with an insulating device identified for the purpose. Wire connectors or splicing means installed on conductors for direct burial shall be listed for such use. 300.5 (C) Underground Cables Under Buildings. Underground cable installed under a building shall be in a raceway that is extended beyond the outside walls of the building. (D) Protection from Damage. Direct-buried conductors and cables shall be protected from damage in accordance with (1) through (5). (1) Emerging from Grade. Direct-buried conductors and enclosures emerging from grade shall be protected by enclosures or raceways extending from the minimum cover distance required by 300.5(A) below grade to a point at least 2.5 m (8 ft) above finished grade. In no case shall the protection be required to exceed 450 mm (18 in.) below finished grade. (2) Conductors Entering Buildings. Conductors entering a building shall be protected to the point of entrance. (3) Service Conductors. Underground service conductors that are not encased in concrete and that are buried 450 mm (18 in.) or more below grade shall have their location identified by a warning ribbon that is placed in the trench at least 300 mm (12 in.) above the underground installation. (4) Enclosure or Raceway Damage. Where the enclosure or raceway is subject to physical damage, the conductors shall be installed in rigid metal conduit, intermediate metal conduit, Schedule 80 rigid nonmetallic conduit, or equivalent. (5) Listing. Cables and insulated conductors installed in enclosures or raceways in underground installations shall be listed for use in wet locations. (E) Splices and Taps. Direct-buried conductors or cables shall be permitted to be spliced or tapped without the use of splice boxes. The splices or taps shall be made in accordance with 110.14(B). (F) Backfill. Backfill that contains large rocks, paving materials, cinders, large or sharply angular substances, or corrosive material shall not be placed in an excavation where materials may damage raceways, cables, or other substructures or prevent adequate compaction of fill or contribute to corrosion of raceways, cables, or other substructures. Where necessary to prevent physical damage to the raceway or cable, protection shall be provided in the form of granular or selected material, suitable running boards, suitable sleeves, or other approved means. (G) Raceway Seals. Conduits or raceways through which moisture may contact energized live parts shall be sealed or plugged at either or both ends. FPN: Presence of hazardous gases or vapors may also necessitate sealing of underground conduits or raceways entering buildings. (H) Bushing. A bushing, or terminal fitting, with an integral bushed opening shall be used at the end of a conduit or other raceway that terminates underground where the conductors or cables emerge as a direct burial wiring method. A seal incorporating the physical protection characteristics of a bushing shall be permitted to be used in lieu of a bushing. (I) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors shall be installed in the same raceway or cable or shall be installed in close proximity in the same trench. Exception No. 1: Conductors in parallel in raceways or cables shall be permitted, but each raceway or cable shall contain all conductors of the same circuit including grounding conductors. Exception No. 2: Isolated phase, polarity, grounded conductor, and equipment grounding and bonding conductor installations shall be permitted in nonmetallic raceways or cables with a nonmetallic covering or nonmagnetic sheath in close proximity where conductors are paralleled as permitted in 310.4, and where the conditions of 300.20(B) are met. (J) Ground Movement. Where direct-buried conductors, raceways, or cables are subject to movement by settlement or frost, direct-buried conductors, raceways, or cables shall be arranged to prevent damage to the enclosed conductors or to equipment connected to the raceways. FPN: This section recognizes "S" loops in underground direct burial to raceway transitions, expansion fittings in raceway risers to fixed equipment, and, generally, the provision of flexible connections to equipment subject to settlement or frost heaves. (K) Directional Boring. Cables or raceways installed using directional boring equipment shall be approved for the purpose.
Reply to
Gerald Newton

Utiities have used splicing cement with two layer of rubber tape and two layers of vinyl tape successfully for years. There are better products out there now. Generally they are heat shrink type.