One thing thay bothers me that I am praying is not a problem. During
the pulling process, some of my wire got "scuffed up". I am positive
it is not throught to the wire, put the plastic looking face has come
off in some areas. I taped with black tape for extra protection. Some
of this is in the part that goes into the panel. For security I
wrapped in black tape for a couple of feet. If the inspector sees this
in the panel, will it be a problem and if so is there an easy way to
remedy it?
It will just pin you as a homeowner, not an electrician but he already
knows that ;-)
He might ask why you did it but he should know what U/L has said about
the jacket. There are several inquiries about this on the various
inspector venues and the answer is always the same. As long as the PVC
insulation (the colored part) is undamaged you don't have to worry
about the nylon cover.