wiring generator

I am interested in wiring a generator to my home via transfer switch. It is a portable unit, not built in. My plan is to run a wire in the attic about 80', from the breaker box/transfer switch, to an outlet in a waterproof box under a covered patio, then use a double male "extension cord" from the outlet to the generator's 50 amp plug, for about another 45'.

My question is this. What size wires should be used to safely move the power that distance? I have been told everything from 4 AWG to 10 AWG, mostly by alleged electricians who at least appear to make a living at it.

During the last storm, I was using 100', 12/3 extension cords to run individual freezers and the like, with no problem.

I am looking to be safe about it. I am not interested in the cheapest thing, and I am definitely not interested in burning my house down. I'd like a little overkill, but on the other hand I don't necessarily want to spend a bunch of excess money for nothing.

Understanding that obviously the larger the wire the better, without going totally overboard, what would be a reasonable and very safe wire size for this project?

Is 6/3 w/ ground SER for the 80' run in the attic, and 6/4 SO for the 45' "extension cord" suitable, or is 4/3 SER and 4/4 SO needed, or is there something totally different out there?

I am not planning on doing this myself, but I do want to be able to make an educated decision regarding what materials to use, and who to use to put it together. Seems like some people may cut corners on materials to get the bid.

Many thanks.

Robert

Reply to
Robert A. Cibiras
Loading thread data ...

You are unsafe there - double male - regardless of wire size.

Use a hard wired male attached at the waterproof box on a short whip, and make a male/female extension for the run from the generator to the box to address that. You'll need to keep the male plug out of the weather, too, so that it doesn't sit there corroding month after month.

You should use #4 copper for the attic run, and #4 SER for the other run to keep the voltage drop within 5%. Here's the math:

You need to keep the voltage drop to 5% or less, (6 volts on a 120 volt circuit). You have a 160 foot run (hot + neutral) in the attic and a 90 foot run outside. #6 copper is .491 ohms per 1000 feet. #4 copper is .308 ohms per 1000 feet. #4 alumium is .508 ohms per thousand feet. (From Table 8 Conductor Properties in the 2005 National Electrical Code)

Using SER aluminum for the 45 foot run (90 feet total wire): #4 aluminum is .508 ohms per 1000 feet. .508/1000*90 = .04572 ohms. At 50 amps, it will drop 2.286 volts. That leaves a maximum of 3.714 (6 - 2.286) volts that can be dropped in the

160 feet of wire in the attic, which means the total resistance of the 160 feet of wire must be 3.714/50 = .07428 ohms or less. At 160 feet, that means .07428/160 = .00046425 ohms/foot or .46425 ohms/1000 feet, which makes #6 too small. You'll have to go with #4 copper in the attic at .308 ohms/1000 feet. It will have .04928 ohms total resistance, (.308/1000*160 = .04928) which means it will drop 2.464 volts. The total drop will be 4.75 volts - about a 4% drop which is within the limit.

You need to address "physical safety" of the extension cord such that cars don't roll over it and damage it, people don't trip on it - that kind of thing.

It would be best if you dug a trench and used permanent wiring to the generator site, and had the male plug on its short whip inside a weatherproof box there. Then a short male/female extension from the generator to the male plug. (My plug is on a 2 foot whip in the garage, and I use an 8' extension to the generator. I run a 30 amp generator, and the wiring is 80 feet (160 in the computation, hot + neutral) of #6 copper.)

Now *if* you are going to trench it, and *if* there is a possibility of using a bigger generator in the future, you should go to a bigger wire size. It will yield no real benefit now and will cost more for the wire, but you *don't* want to dig an 18" deep 45 foot trench more than once.

Ed

Reply to
ehsjr

Don't forget the approved transfer switch. Thousands of linemen will thank you when you don't accidentally electrocute them.

Charles Perry P.E.

Reply to
Charles Perry

The others have pointed you in the right direction. Sounds as if you have not gotten the transfer switch yet... So look into a 4 pole switch, so you can switch the neutral. The reason I suggest this is because of the distance between the generator and the service. What have you done to ground your generator effectively?

Running four wires will assure that everything will work correctly. The generator creates a new neutral. Hence the reason I like the 4 pole transfer switches. Nothing says this as to be an automatic switch you could use a 4 pole double throw switch as long as it was service rated.

formatting link
This one is used and over sized for your application. Offered as a hint what to look for. If your generator is only 50 amps you would be able to install a 60 amp switch. CH used to make some residential stuff. I never used it or installed it.

Reply to
SQLit

| The others have pointed you in the right direction. Sounds as if you have | not gotten the transfer switch yet... So look into a 4 pole switch, so you | can switch the neutral. The reason I suggest this is because of the distance | between the generator and the service.

Are you also suggesting switching the EGC in addition to the neutral, or did I miss the OP saying his home was on three phase power?

Would it be proper (compliant with code, and actually safe) to have a 4-pole disconnect on a single phase (line, line, neutral, ground) service entrance? I get enough heat from people by merely suggesting that I might disconnect the neutral (in addition to the 2 hot lines).

Reply to
phil-news-nospam

Reply to
operator jay

The OP would be well advised to use a generator inlet box such as the ones shown at

They provide a fixed male plug installed in a weather proof box.

-- Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison

Reply to
HorneTD

OOPS,, fat fingered that one I meant 3 pole.

I am pretty sure that disconnecting the ground execpt in testing situations is not allowed.

Sorry for the confusion

Reply to
SQLit

formatting link

The transfer switch has to be sized for the larger of the generator capacity or the utility side circuit feeding it. If the switch is going to be installed on the service entrance, ahead of the main circuit panel, it will have to be 100 or 200 amps. A 60 amp switch feeding a subpanel would limit the emergency circuits to a

60 amp feeder.

Mike

Reply to
Mike Lamond

Thanks for all the info. I have obtained 4AWG wire for the project. The final piece of the puzzle to avoid the double male plug is a replaceable female receptacle for one end of the extension cord to plug into the inlet box refenenced above. The male ends are a dime a dozen at Lowes, Home Depot, etc. The female is not. I have located 50 amp extension cords for RVs, though generally only with 6AWG wire, and no more than 30' long, which have the female end on them, so I know they exist. I have found replacements for a 30 amp female receptacle at

formatting link
, but no 50's.

Anybody know where I can locate such? I have tried the electrical supply houses in town, and have found the closet thing on the internet on RV sites.

Thanks

Robert

Reply to
Robert A. Cibiras

You're looking for something like this?

formatting link
your electrical supply house the information. You want a "50 amp cordset connector, Pass & Seymore model CR6364" or equivalent. Perhaps they can order it for you.

Two good sites:

formatting link
formatting link
You can order it online for $70.00 here (watch out for line wrap):
formatting link
here for $45.00
formatting link
here for $43.00 (watch the line wrap)
formatting link
Check all the sites to make sure of what you are getting.

Ed

Reply to
ehsjr