Re: Heatsink cooling

Let's say that I have a source of about 800-1000 watts (two dual IGBTs

> inverting 200 amps). They should run relatively cool, to stay safe say > under 80 C. I have a heatsink that is about 6x13 inches and weighs > perhaps 12 lbs. I am cooling it with a fan mounted right next to the > ribs, pushing air along them, the fan is about 20 watts. Ambient temp > could be quite hot, say 40 C (inside welding machine). Would you say > that this amount of cooling should be enough? I will have a overheat > switch mounted on the sink, so, hopefully, worst case would be a > inconvenience of having to stop welding, but I would like to have some > idea of adequacy of this setup. > > i

What's the CFM (cubic feet of air) rating of the fan? And what's the surface area of the heatsink? (Material of construction of the heatsink?)

1 kW of heat to dissipate... have you considered a water-cooled system?

Is this a system you're building yourself, or is this setup on an off-the-shelf piece of equipment?

Cross-posting to sci.engr.mech, they should be able to contribute more ideas.

Reply to
onehappymadman
Loading thread data ...

1kW is nothing really. My amps can generate about that much ( in 2u of 19" rackmount ) and I get rid of it with a max heatsink temp of 95C with 2 80mm 'boxer' style fans.

Graham

Reply to
Pooh Bear

That's very nice to know PB. 1 kW is a bit of an overestimation. 800 watts would be the maximum (200 amps x 2 volts voltage drop x 2 sides of the bridge), and welding would not be continuous, as well.

i
Reply to
Ignoramus18299

Back in the office I have a neat little equation for temp rise in airflow vs energy absorbed. You can do it from first principles but it may come in handy. I'll post it later. It shows importantly that for certain temp rises vs watts you need a given mimimum airflow.

Graham

Reply to
Pooh Bear

energy absorbed. You

Thanks! Yes, I would like indeed to do some calculations. Now that I am packaging stuff for real installation inside the welder, I want to avoid making stupid avoidable mistakes.

I made some pictures last night, of the heatsink assembly with some comments.

formatting link

i
Reply to
Ignoramus2491

Found this nice article:

formatting link
Will check it out. Turns out that my heatsink with glued in fins is the highest performance heatsink.

i

energy absorbed. You

Reply to
Ignoramus2491

I used this calculator:

formatting link
Volumetric Flow Rate m^3/s 0.06 Number of Fins 13 Fin Width m 0.001 Fin Length m 0.3 Fin Height m 0.13 Sink Width m 0.12 Fin Thermal Conductivity W/mK 237

Result: Thermal Resistance C/W 7.46266e-02

So, for a continuous 800 watt load, the temperature rise would be

56C. That's probably acceptable. In reality, my load would be less than 800 watt (current lower than maximum, non-100% duty cycle in a welder). So, I am not worried about adequacy of my heat sink assembly. i
Reply to
Ignoramus2491

Here's the info I had in mind. It conveniently mixes units so as to use the ones that are hopefully most accessible.

Graham

Heat transfer equation from Sunon ( fan manufacturer )

Q = Cp . W . T

Q = Amount of heat transferred Cp = specific heat of air T = temperature rise W = mass flow

putting in the relevant values I got to this..................

Air flow required ( CFM ) = 1.76 * power / temp rise ( degrees C )

Worked example e.g. 200W and delta T = 50C

gives 1.76 * ( 200 / 50 ) = 7 CFM

Reply to
Pooh Bear

ones that are hopefully

Thanks. I also tried to find some place with a calculator and found something nice. Below is a copy of ,y text file with a little detail of these calculations. It looks like my setup is just about adequate for 100% duty, which it will obviously not see due to application (welder).

formatting link
Heatsink calculations:

Size 7x12 width, 5" depth, 10 fins.

According to

formatting link
Volumetric Flow Rate m^3/s 0.06 Number of Fins 13 Fin Width m 0.001 Fin Length m 0.3 Fin Height m 0.13 Sink Width m 0.12 Fin Thermal Conductivity W/mK 237

Result: Thermal Resistance C/W 7.46266e-02

Reply to
Ignoramus20351

ones that are hopefully

That looks about right. But that assumes perfect coupling from the heatsink to the air stream, which doesn't happen.

This gets complex, and I don't really understand it, but it's something like...

If the fins on a heatsink are few and far between, the 7cfm will zip through easily and not pick up much heat. So if the sink is dissipating the 200 watts, the air exit temperature will certainly be

50K above intake (by conservation of energy) but the heatsink may be a lot hotter. Imagine half the air being in good contact with fins, half zipping through unaffected, and the halves mixing at exit, averaging +50. The heatsink only contacts half the air, so it rises +100.

If the fins are very dense, coupling from sink to air will be good, but you'll develop a lot of back pressure, and a "7 cfm" fan won't move 7 cfm, so again the sink temp rise will be above 50.

My working theory is that you get the best heat transfer if the heatsink restricts the fan to delivering about half its rated cfm. And the fins should be nearly isothermal (ie, not long and skinny) because cool fins restrict flow without coupling heat very well.

Anybody know more about this?

John

Reply to
John Larkin

I wish more people would do what you do - post updates of the progrees in your project. You do a very good job of keeping interested people informed. Thanks!

Ed

Reply to
ehsjr