VFD as 3Ph shop supply

Feb 06, 2009 88 Replies

Guys, what are the limitations, precautions, or dangers of using a VFD set to 60Hz as a "general" 3-phase shop supply.



Say I had a total of 15HP worth of motors in the shop. If I installed a



15-20HP VFD, would there be any inherent dangers/damage potential in switching motors in and out of circuit?

Can they work that way, or must they be connected to a motor during their ramp-up time?



Tnx



LLoyd


Wiring length.

You can damage the drive by switching big motors on it, and also, long wiring may create huge voltage spikes and damage your motors and general insulation.

You can somewhat mitigate the effect of wiring length, any VFD manual talks about this. Basically you would need to set up an inductor.

Ignoramus7868 fired this volley in news:4K2dnaxcT6DL1RHUnZ2dnUVZ snipped-for-privacy@giganews.com:

manual

Yeah... some vendors call them "surge arrestors", but that's not quite accurate. I understand how to do that. It wouldn't even be much of a stretch to install "soft start" features on any motor that started with no load.

The "long wiring" in my shop would be a maximum of 25', if I centralized the VFD.

LLoyd

All of what Iggy said, plus larger VFDs often won't accept single phase power input, and smaller VFDs are pretty reasonably priced these days and I'm pretty sure using individual VFDs will cost less that buying one monster single phase input capable VFD.

And it will be much more convenient.

I have very reasonably priced VFDs 3-5 HP nameplate rating for sale. They work with single phase with some derating

Can you get VFDs that large that also accept single-phase input?

Assuming that you can, I think you can switch motors in and out so long as there is at least one large motor always connected and spinning. In other words, the large motor acts as a rotary phase converter and buffer, absorbing the surges caused by motor switching. The real test is when someone plug reverses a big machine somewhere. The large motor must be big enough to absorb this.

Put the large motor near the VFD, and feed the rest of the shop from the motor terminals, so the wiring beyond the motor isn't really sensed by the VFD.

Joe Gwinn

Ignoramus7868 fired this volley in news:kaKdnfpzlNCuzBHUnZ2dnUVZ snipped-for-privacy@giganews.com:

Links? LS

Here the 5 HP model. I also have 3 HP.

formatting link

Ignoramus7868 fired this volley in news:UZSdnQFm9II7xRHUnZ2dnUVZ snipped-for-privacy@giganews.com:

Ok... that's nice, but I can't seem to find the ebay listing, and don't know your "store" name, if you have one.

LLoyd

Sure, some Yaskawa models that will run on single phase are available up to 30 or 40HP. I installed 2 10HP Emerson drives last week on single phase input. 240V drives from that series go up to 30HP.

I don't see the point. You're using a significant fraction of the VFD's capacity to run a motor that could serve the same function running as a simple RPC. In other words, the VFD isn't doing anything useful.

I do not currently have them on ebay.

Polyspede turns out a series that goes up to 30HP rated 3ph output from single phase input. I have the 15HP model.

formatting link

formatting link
>

Yes, same type I bought. The one I installed on my Bridgeport is performing well.

Well, the length is the sum total of the length of all wires. So if you have five circuits, each is 20 ft, then your length is 100 ft. The issue is cable capacitance. More cable, more capacitance.

formatting link
>>

Delightful. I have a bunch of people who put them on mills.

Ignoramus7868 fired this volley in news:LIydnYXnD6YZ-xHUnZ2dnUVZ snipped-for-privacy@giganews.com:

So, you tune it with the appropriate series inductor. That part isn't a tough one to overcome. Of course, one could also run separate wires at suitable spacing. Twisting wouldn't have much effect at 60Hz.

LLoyd

Iggy I don't have any experience with VFD's. I run a rotary converter on my cold saw and grinding table. I have several other applications that I could use a VFD on. A bandsaw and drill press and Atlas lathe are a few. How quickly can the speed be changed? Do you program the speeds you want and just push a key or two when you need a different speed? Steve

You can, and they will cost you big bucks. About $1,000 for 10 HP.

Whether you can get a 3 phase rated high HP VFD, and coax it into taking single phase input, is a very big question. I will soon work on it.

This depends on their relative sizes, I think that Lloyd wants to have only one motor operating at any given time.

You can connect a potentiometer to one, and on/off switch, and use that for switching and speed changing.

formatting link
>

Iggy, couple of questions about your 3hp VFD. I have three phase from the utility company and would like to use the VFD on my lathe (LeBlonde, 13" 2hp, I think) simply for speed control and 'quick-stop'.

1) will your 3hp VFD take three phase input? 2) will a 3hp VFD have issues with a 2hp motor (mismatch)? 3) you don't list a price?

Thanks, Ivan Vegvary

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required