Motor Star / Delta question

Nov 15, 2006 26 Replies

I've just completed this very task. I won a 2hp inverter from Drives Direct on fleabay for =A3105, got him to provide a forward/off/reverse switch and a speed pot. My motor is a very old Brook Gryphon 1hp that I've just had rewired to Delta and given a refurb by my local rewind place. The instructions with the inverter are amusing in their lack of detail, I basically figured it out from the rough diagrams included. Pretty straight forward to wire it all up and job done. Just waiting for an IP56 junction box thing to arrive through the letter box so I can mount the switches neatly and I'll be all set! If you'd like to see some pics let me know and I'll get the camera out.

Cheers, Rob

John...I don't what they are paying you but it's not enough!

Thanks for the explanation.

John B

Thanks to all for their help and advice with the motor and inverter questions.

A Telemecanique ATV 11 turned up from RS this morning and I have spent the evening connecting it all up on the bench to test. It runs nicely so I will box up the speed pot + switch and stick it all on the ML7 tomorrow.

There's one thing I noticed and that's the inverter will trip the house RCD on switch-on from time to time so it will probably get left on all the time.

Duncan

I hope leaving it on all the time works for you!

I used to leave my Siemens VFD on all the time because it too regularly tripped half the power in our house when switched on. What was worse though is when I left it powered up constantly it frequently still tripped the RCD, seemingly randomly, but usually middle of the night, middle of the day, and whenever else it felt like it.

I have got round the problem in the short term by plugging the VFD into a socket wired into the non RCD protected side of the consumer unit but would really like to get to the root of the problem.

Ian Phillips

inverter

regularly

Inverters, like switch mode power supplies, have a high leakage current due to capacitive effects and the high frequencies that they switch at.

AWEM

Often made worse by built-in EMI filters. The makers often say that they shouldn't be used through an RCD, or only be used with a particular type of RCD, which works with DC as well as AC.

I have an ABB inverter for which the manual recommends disconnecting parts of the internal filter for use with an RCD. They say to contact ABB for instructions. Needless to say, they were initially baffled when I asked! It would trip the (80mA) RCD every time, but now it's fine with the filter partially disconnected.

Cheers Tim

Dutton Dry-Dock Traditional & Modern canal craft repairs Vintage diesel engine service

I have a Teco 1HP inverter for my pillar drill and the manual says any RCD must be >200mA and operation time >0.1sec. I think this is probably quite insensitive, I recall we had ones at work in an office that were

30mA for 30ms and they had to change them to 80mA. Maybe you just plug in a different RCD module ??

But then I don't have an RCD consumer unit - so no problems for me.

Steve