problems with chattering contactors

I have a three phase forward/reversing drill press that runs in each direction. However the contactors for each direction recently started
buzzing or chattering rather loudly. I have already checked for obvious wiring problems. What are some causes for the loud buzzing? Sincerely, Steve
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Delamination of the contacts is the usual culprit. Are the contactors getting hot?
Eventually the contactors will fail (your drill press won't work) and you'll have to get them replaced.
HTH, Cameron:-)
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Dirty pole faces ?
sQuick..
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
sQuick wrote:

A common problem no less, but not caused by bad contacts of the chattering contactor! Check the control contacts upline from the chattering Contactor (switchs or relays). Most likely, too much resistance in the operating coil circuit which causes low voltage & high current. use a meter to measure the inrush current.