I am controlling a dc motor via a servo and I am using a PID a controller as my controller. The servo position at 600 is when I achieve the max speed of the motor and at 2900 is when the motor is stopped. How do I handle this in the implementation? Any ideas?
Didn't find your answer? Ask the community — no account required.
Connect another servo in parallel. If both twitch at the same time, look at the...
T
Tim Wescott
So when you command 600 whatevers to the servo the motor is going maximum speed, and when you command 2900 whatevers to the servo the motor is going at minimum speed? What ever is your unit of measure?
The conceptually easy way to handle this is to translate your motor speed commands into servo commands, e.g. if your maximum speed is
12000RPM then you calculate the offset and slope using good old y = ax + b:
y1 = 2900, x1 = 0 y2 = 600, x2 = 12000
Then b = 2900, and a = (600 - 2900) / (12000 - 0) ~ -0.192. Then make a regular old controller.
The least-processing way to handle this is to operate your controller in reverse -- bring your speed (or position) command to the subtracting port of your summing junction, bring your speed (or position) feedback to the adding port, and have at it. All the signals in your controller will be negative of what intuition says they should be, but the system will work fine.
B
bxa132203
B
bxa132203
Thanks much for the info. I'll try it.