3 Phase motor running current

Jan 13, 2006 4 Replies

We commissioned 6.6KV 3PH Motor. During no load run we noticed that the motor was drawing un balance current. We had balanced 3 phase voltage. Please clarify why the motor is drawing unbalance current.



Regards A.H.Rajagopal



Not sure. You could shoot us some numbers, the phasors for the three phase currents and the three line to line voltages. Maybe you had some neg. sequence voltage?

j

The first thing that comes to mind, is how are you measuring the voltage and current? Are you using 2 PT's or 3 Are you using 2 CT's or 3 Are you above 10% loading on the circuits?

is that really kilo-volt or kilo-watt?