| It currently is on 3 Phase 440 with the same 220 on one, and two with | 110. It is directly wired through a fuse box to the electric circuit. | I will check tomorrow on the motor plate and let you know.
I assume you mean 120, 240, and 480 respectively (the standard voltages)
One big confusion here is just how your source of power is configured. You don't get 120 out of a 480 volt system without some kind of other transformer being involved.
Which type of 480 volt three phase power do you have:
- 480/277 wye/star, with neutral provided (4-wire)
- 480/277 wye/star, but the neutral is not provided (3-wire)
- 480 closed delta, corner grounded
- 480 open delta, common corner grounded
- Something totally bizarre
Where is the 240 volts coming from?
- It's own separate system
- A center tapped neutral on 480 delta (480/416/240)
Where is the 120 volts coming from?
- A center tap and 2 corners on a 240/208/120 delta system
- A single phase from a transformer separate from the 480
- A single phase from a transformer fed by the 480
- An autotransformer
Perhaps either the motor or the controller needs a 4-wire wye three phase system. If this is a wye/delta soft start controller, then it will need a wye source, and you will need to power the motor with 6 wires.
Either someone experienced with this needs to take a look, or you need to describe everything in excruciating detail (including where every wire goes to and comes from). You may also need to have a volt meter handy to check the voltage difference between every possible pairing of wires.