7 useful question about - MCC - Lighting pole - Protection relay - Cable routing

Hi I am an Electrical engineer.Dont worry about me.Thanks of SQLit. My english is not fluent.

7 Questions:

1) In zigzag arrangement of street lighting poles if the lamps are 400Watt the distances between poles are 45 meter , but 45 Meter between two poles in same side or between two poles in different sides ?

----------

2) Is the HVAC system , necessary for M.C.C ( Motor Control Center ) panels room ? ( only MCC & switchgears , not control panels or any PLC ) is this necessary for capacitor panels ? ( Room with HVAC system and airlock doors).Where is the usual place of MCC panels if the control room is separate from switchgear room?

-----------

3) Where is the exact location of protection relays in a site ? (400v-3300v-66kv) How much is the bulk of them ?

-----------

4) Whats the kind of cables between protection relays ? How much core and pairs have them? Where is the routing of them ? in same ducts of power cables or ducts of control cables? Whats the voltage and A of them ?

-----------

5) Preparing of the logical single line ( One line) between relays is the task of electrical department or instrument department ? Can you send me an example?

-----------

6) In a site we want to carry a 3300 v ( 1.2 MVA ) power between two building, can we use Air line or we should use cable trench ?

-----------

7) the capsulated SF6 cables is fabricated in 12Meter sections.can we cut them to smaller parts?

----------- My E-mail: snipped-for-privacy@yahoo.com Thankyou.

Reply to
eoots2000
Loading thread data ...

Depends on the light spread of the fixtures and intent of the designer. Is the intent to have spots of light or a continuous band of light?

Depends on the enviroment. An HVAC will definately keep the equipment cleaner. Which has a lot of benifits. We mount capistiors on the roof or on the ground away from everything and every one. I have seen capisitor cabinets grenade several times. Not a pretty site if they were inside.

Have to follow the code and installation on this one. Line of site and 20 feet is the max for a disconnect here in the USA.

What voltage? what installation condition? Typically controls are limited ampreage -----------

-----------

No enviroment information, Overhead is usually cheaper.

Can you please provide cut sheet/manufacture for SF6 cables? I have never seen any. I would like to learn about them. Probably if you have the termination, reclaiming and testing tools for the job. SF6 is frowned on in some places that I have been. Getting a fresh supply of SF6 can be difficult and the last time I looked into a fresh supply, the only place that I found was Russia.

Reply to
SQLit

I have found that you get much more feedback from Usenet if you break things up and not try to get too much in one message.

I gave up on question 3. Not that I could add anything useful anyway.