I have a 20 amp UPS I want to use with a 15 amp electrical circuit, safely. What I need is an adapter that goes from 5-20R to 5-15P and has a built-in fuse for 15 amps, so as to never overload the installed circuit.

Does this exist off the shelf, and if yes I would appreciate any references to where I might purchase it.

Reply to
Will
Loading thread data ...

Reply to
Long Ranger

Just how are you going to persuade the UPS not to draw over 15A, eg when first switched on? What type of UPS is it?

I'm not that familiar with US mains wiring, but won't this circuit already be individually fused for 15A, at the local distribution board? So, what exactly, is the built-in fuse going to protect, in addition?

Thus I can't see why anyone would manufacture such a thing.

You can, presumably, wire your own "adapter lead". Or just take the plug off and fit a 15A one.

You can also write to the UPS manufacturer and ask their advice regarding running it from a 15A service, on light load. I would suspect that they will recommend that you don't. BICBW

Reply to
Palindrome

This is a SmartUPS SU3000NET 5U rackmount. Apparently it does not draw more than 15 amp when switched on because we have one in a test lab that powers on with a 15 amp circuit and never trips the breaker on power on.

Yes, there is a fuse on the circuit at the panel. But in this case I'm just trying to add an extra level of protection, because we are knowingly plugging in a device that could in theory (but probably never in practice) overload the circuit.

In any case, sounds like it would be a custom adapter.

Reply to
Will

You can waste your money on a power strip with a

15 amp breaker. That's the closest you'll get to the adapter you describe. It won't make things any safer.

No adapter is needed between a 5-20R and a 5-15P. The 5-15P mates perfectly with the 5-20R; the extra slot in the 5-20R is for identification purposes only. You don't have a 5-20R if you have a properly wired 15 amp branch circuit.

There is no way to plug a 20 amp device into a 15 amp circuit "safely".

Ed

Reply to
ehsjr

I rather think that the OP intends that the device wont ever draw 15A (let alone 20A) in normal use. Mapping protective devices to the SOAR of the circuit should allow it to be used "safely". One suitable device may easily be enough.

BTW, it was the adapter lead that was to have the 5-20R...

Reply to
Palindrome

OK, a line-interactive unit.

Anything you plug in could, under fault conditions, present an overload. The only thing special about what you plan is that the UPS could easily present a *small* overload over a prolonged period. Which is a pretty rare "fault". You need to ensure that your protective device can discriminate against this small overload and clear the circuit. Fuses are good with large overloads but pretty ineffective with very small ones.

But it is certainly something that could be done *safely* - with the corect protective devices present.

Reply to
Palindrome

Wouldn't matter if he put in a 15 amp fuse. The requirement here (US - National Electrical Code) is that no single device plugged into the circuit may draw more than 80% of the branch circuit rating. If the device is rated at 20 amps, the NEC doesn't care about whatever Rube Goldberg he rigs up. The device rating itself can't be more than 12 amps, regardless of what is in some external adapter.

But set that aside for a moment and consider that the branch circuit is certainly not dedicated to a single receptacle. Adding a 20 amp device that doesn't draw over 15 amps (because the op says so) is still screaming for an overload. The other outlets on the 15 amp branch easily allow an overload to occur, even if his device never draws over 15. He's got a 20 amp rated device which is supposed to be installed on a *30* amp branch (to meet the 80% rule) and he's going to install it on a *15* amp circuit??! No way that can be considered safe.

Yes, but it doesn't matter. The 5-20R is no different functionally than a 5-15R. There is absolutely no need for an adapter with regard to 5-15P and 5-20R. His device has to have a plug that mates with a 5-20R. If it mates with a 5-20R, it will mate with a 5-15R. But this suggests that the device has already been, or is planned to be, illegally modified. If it is truly a 20 amp device, then its plug should be a 30 amp twist lock, not a straight blade

15P.

Ed

Reply to
ehsjr

I can't agree that it can't be made safe. For example, if the branch protection fuse was replaced by a 1A, where, exactly is the risk? It may not be code, but it is certainly possible to make it safe.

There you go, as I said, I am not into US electrics. I had thought that a 20R would take either a 20P or a 15P - but that a 15R wouldn't take a

20P. And that this was rather the point of the OP. IIUC, he wanted a lead with a 20R on one end, to take the plug from his UPS and a 15P on the other, to fit his wall socket. With a protective device in the middle, to "make things safe". If that protective device was a 1A fuse, where's the danger? You seem to be saying thatit could ahve a 12A fuse and still be safe, although not "legal".
Reply to
Palindrome

If I understand the OP, he has a UPS with a 5-20P. This will not mate with a

5-15R. See:

first 2 photos at the top.

At least that's the way it appears in my head... (c:

Reply to
DaveC

I believe the device was manufactured with the 5-20P, and is not really a "20A" device, but something that draws more than 12A (thus ineligible for the 5-15P) but no more than 16A, and because it draws no more than

16A, is eligible for the 5-20P.

Umm, no. The 5-20P has one vertical and one horizontal blade. It will not fit into a 5-15R, the "normal" US outlet, which has two vertical slots. The 5-20R has a T shaped slot, and will accept either a 5-15P or a 5-20P.

To the original poster: Check whether the outlet you want to use is on a 20A circuit, and is wired with #12 wiring. If so, you can simply replace the 5-15R outlet with a 5-20R, if you can replace an outlet safely.

Also, FWIW, a possible reason for the 5-20P is the UPS was designed to power devices drawing up to 16A total, but won't draw that much current without such a load.

Reply to
Michael Moroney

That's how I understand it too, and he wants an adapter with a 5-15P and a 5-20R. According to APC's website, the SU3000NET has a

3000 V-A rating and a L5-30P plug. That makes sense for a unit that can draw 25 amps. The 5-20P is the wrong plug in the first place, and the OP might as well change it to 5-15P if he can get the #10 AWG conductors into a smaller plug. I've seen in done before (my input was Not Needed). None of this makes it any more code compliant. What the OP really needs is to reinstall the right plug and connect it to a 30 amp circuit with a single L5-30R receptacle.

By the way, per NEC 210.21(B)(2) and 210.23(A) and (B), the 80% limit for a cord-and-plug connected load only applies to 15, 20 and

30 amp branch circuits with two or more outlets or receptacles. I read that and the first paragraph of 210.23 to allow connecting the full load on a branch circuit with a single receptacle.

Mike

Reply to
Mike Lamond

That's stretching things all to hell and back, and still wouldn't make it safe. It would just blow fuses. That would lead to extension cords draped all over the place, as the 15 amp branch wouldn't support much at all. The same effect as your 1 amp fuse can be achieved by unplugging it.

You seem to be saying that you can violate the safety requirements and still be safe, while I'm saying that violating the safety requirements automatically means it cannot be considered safe.

That is correct. But he's got a 20R and a 15P - at least that's what he said. From a 20R to a 15P does NOT require an adapter. Others think that he is referring to the connectors on the adapter, not the receptacle and plug he already has, and they may have the correct idea, while my idea of what he has may be incorrect.

And it still doesn't matter. What he is talking about is *unsafe*. His premise that it doesn't draw more than 15 amps is: "Apparently it does not draw more than 15 amp when switched on because we have one in a test lab that powers on with a 15 amp circuit and never trips the breaker on power on." His statement is that this is a 20 amp device: "I have a 20 amp UPS I want to use with a 15 amp electrical circuit, safely. " When you look up the device, it requires a *30 amp circuit*. The manufacturer's rating trumps whatever the op, you or I think is safe.

Fuses or breakers do not make a circuit safe. What makes a circuit safe is proper design and implementation. The fuse or breaker is there to protect against some defect that would make an otherwise safe circuit unsafe, and when it blows/trips it is telling you there is an *unsafe* condition. In the case the op requested, that unsafe condition is designed in to the circuit.

That's bending things all to hell. Might as well leave it unplugged.

I don't mean to make that impression, it's too "soft". No outboard device can make it safe. If the device itself contains a 12 amp fuse as part of the original design, then it meets safety requirements for installation on a 15 amp circuit. (But in that case it would not be rated for 20 amps.) If it does not meet safety requirements, then it is not safe.

Ed

Reply to
ehsjr

Yes, you are correct. I was sloppy with my wording. I was speaking with regard to a 15P, which has to mate with a 20R.

The problem is actually very simple, and a lot of respondents were sucked in. That model UPS is designed to be installed on a 30 amp circuit. Unmodified, it has a 30 amp twist lock plug. The op's original post mentions a 20 amp rating, a 5-15P plug, and a 5-20R receptacle, which had the effect of diverting attention from the original design of the device.

No qualified engineer in his/her right mind would authorize the proposed installation with all the facts in view.

Ed

Reply to
ehsjr

Exactly right. I've never seen a 15 amp dedicated circuit, thus my comment that the branch circuit is certainly not dedicated to a single receptacle. 'Course that doesn't mean there are no 15 amp dedicated circuits anywhere in the world, and it is possible the op has one. But that doesn't change my thoughts on the matter.

Ed

Reply to
ehsjr

Nope, what I am saying is that you can violate safety regulations and still be safe but you cannot violate safety principles and be safe. The regulations were drawn up based on the principles, but of necessity had to present a simple set of rules to be followed. A technician has to work to the set of rules. An engineer has the depth of understanding of the underlying physics needed to both draw up the rules and determine when one or more of them can be waived.

As I wrote previously, the safety requirements were drawn up by engineers, for the blind obedience of technicians. Engineers wrote the book and can re-write the book. And often do - safety requirements are not immutable but are subject to constant change. What never changes is the underlying principles - the physics the links action to effect.

It isn't inevitably unsafe to breach safety regulations - even if it is inevitably unlawful to do so.