Calculate demand from periodic power readings

Jul 23, 2006 9 Replies

Can anyone point me at some information on calculating demand from periodic readings?



For example, if I have a system that takes actual kW readings from a meter once per minute, how do I calculate the:



1) 15 minute sliding/rolling demand
2) 15 minute block demand

I have some information that this is as simple as averaging the readings but I don't believe this is 100% correct. I would like some documentation from a authority like IEEE. I am a member of IEEE but I can never seem to find what I need on their site.



Chuck



I don't have an exact link to what you want, but I believe you can find an explanation on :

formatting link

Charles Perry P.E.

I could not find anything on the subject. It was an interesting site though.

I have been searching for days and I can't understand why this information is so hard to find. All digital demand meters must use this formula for demand calculations. Many energy management systems must also use this calculation unless they read demand straight from the meter.

There must be documention on the formula someplace.

Chuck

First of all, if you are reading kW (rather than accumulated kWh), you aren't reading the same thing that revenue metering uses for demand.

15 minute kW demand is calculated by measuring the kWh used in 15 minute periods and dividing by 4. In other words, 20 kWh consumed in one 15 minute period equals 5 kW demand. If this is calculated once every 15 minutes, this is the block demand.

If you store the kWh readings every minute, look back in memory for the reading 15 minutes ago, subtract the two and divide by 4, this is a sliding or rolling demand.

If your metering is measuring kW (instead of kWh), you have to integrate the readings. The sample rate used will influence the accuracy of the resulting figures, depending on the characteristics of the actual load fluctuation.

In the end, the definition of figures used for revenue calculations should be traceable from the filed tariffs.

Interesting, I didn't know demand was calculated from energy values.

By the way, mathematically it seems like that should be multiply by 4 rather than divide by 4. Consuming 20kWh in 15 minutes, I would think you would 'project' the use of 80kWh in an hour, for a 'demand' of 80kW.

Where I am, demand is based on kVA rather than kW.

j

I looked up some very comprehensive tariff schedules

formatting link
I did not find anything on the actual calculation of demand. It did say what kind of demand they used for each tariff schedule (block, rolling, etc.) but not exactly how to calculate the number.

Paul, you are correct that I am trying to calculate demand from periodic kW readings. My concern and something I have seen in real life is that the kWh readings don't change very rapidly so this can cause the calculations to have a low resolution for small loads.

For example if you have a variable load that consumes 5kWh every hour, the kWh meter will only flip over a new number approximately once every

12 minutes. So in most 15 minute windows I will calculate 1 kWh of use or a demand of 4kW. However, in some 15 minute windows I will calculate 2 kWh or a demand of 8kWh. Over time of course, this all balances out to the correct number but plotted on a graph, it is distorted. Many customers want to look at these charts for analysis purposes.

With many digital power meters, the kW reading goes down to a resolution of 0.001 kW or 1 watt. I realize that if a take a set of kW readings every minute, I can only approximate the demand by feeding the periodic readings into a calculation but I feel this is better for analysis purposes than using kWh readings.

Any suggestions would be appreciated.

Chuck

It is for integrating demand meters. Thermal demand meters measure kVA (they are essentially voltage compensated ammeters with a time constant that approximates a 15 minute demand. Back in the old days, these were cheaper than integrating meters, but in my area, there is only one utility that hasn't ripped out all of its mechanical, manually read meters with remote metering systems. Once the microprocessor is in, the cost of integrating metering is essentially zip. They can (but don't yet) report back 15 minute demand figures even for residential meters.

You're right. I think 'divide kWH by time to get kW', but the time in this case is 1/4, not 4.

It depends on what you're being billed for. Large commercial and industrial customers (where I work) are assessed a demand charge per kW, not kVA. They are also assessed a reactive power charge per kVARH. One utility has set its real and reactive demand charges for HV (transmission voltage) service customers to be the same, so there its possible to base charges on kVA. But for customers of this size, the bills are large enough to justify integrating metering.

Actually, what goes on in the meter is as follows: A CL200 meter (mechanical disk type used for most residential services) has a meter constant of 7.2 Wh per disk revolution. So, for a 5 kW load running for

1 hour (5kWh) the disk will rotate 695 times. The dial reading is produced through a gear reduction system and is intended for reading over weeks or months. But the microprocessor (which handles remote reading) actually counts disk rotations. This gives a much finer resolution which can be used for calculating demand.

Its better than counting disk revolutions, but not by much.

If you have a digital power meter already, then that's the way to go. But why limit yourself to one reading a minute? Take one every second, or 5 seconds. Computing power is cheap.

I am not interfacing with spinning disk type meters. I deal with sub-metering where the metering function of the meters is not great. These meters are all electronic. Furthermore, I don't care if the readings are kW or kVAR as the calculations would be the same to calculate demand.

And you are correct that the meters can perform volts, amps, and kW, but many times do not produce kWh readings. And if they do, the kWh readings are sufficient for once a month readings but not 1 minute periodic readings because of the depth of the resolution.

Ok, so to summarize, I have determined that I should take one minute or quicker readings of kVA or kW and log them to a database. I would then do the following on the data:

-15 minute kW demand is calculated by measuring the kWh used in 15 minute periods and multiplying by 4. In other words, 20 kWh consumed in one 15

minute period equals 80 kW demand. If this is calculated once every 15 minutes, this is the block demand.

-If you store the kWh readings every minute, look back in memory for the reading 15 minutes ago, subtract the two and divide by 4, this is a sliding or rolling demand.

These two methods sound very easy to implement from a software side. But these mathematical methods don't simulate the old elecro-mechnical demand meters: do they? Is this method legal for billing calculations?

Paul mentioned a "with a time constant that approximates a 15 minute demand". Is there someplace this constant formula is documented? I believe what you are referring to is the 90% reading after fifteen minutes to simulate thermal demand. Is this method not used for billing calculations anymore?

Also mentioned, I can take the readings fairly quickly but there are other considerations like bandwidth between the meter and computer. Also, the local computer/collector may not even be a full computer with a lot of power.

formatting link
I agree however, that taking the readings as fast as possible will allow more accurate readings.

Thanks for all the help. I am new here but this seems to be a very helpful newsgroup.

Chuck

Ah...

But storage or data transmission is not always cheap. Working a project in the DTE area, we had to compromise since the meters we were using used POTS lines to 'phone home'. At just 9600 baud, we wanted to be able to download

24 hours of data in a 'reasonable' time from each industrial customer that had signed on. And, if a meter failed to 'phone home', we wanted it to keep on recording data for up to three days (72 hours) without losing data. One second sample rates would have 'killed' us on that.

daestrom