. Damage to a TV obviously depends on the TV and the overvoltage.
The IEEE guide goes on a length how the protected load can be connected across the MOVs or connected to the incoming line. If connected across the MOVs, the protected load will be disconnected when overheating MOVs are disconnected on failure. I suspect that MOVs will overheat and be disconnected before high current operates overcurrent devices. A few plug-in suppressors will disconnect on overvoltage. .
. The intended point was that MOVs don?t normally fail by "open[ing] back up". .
. MOVs, like anything else, will fail. The normal way they fail is low resistance .
. It isn?t a design. It is the way they work. .
. Why would you think UL isn?t testing for safety risks.
Didn't find your answer? Ask the community — no account required.
Solution below! Gas units operate partially on natural convection, and...
B
bud--
formatting link
> | has an illustration of a surge coming in on a cable service (pdf page
. A lot of houses have signal entrances too distant from power services. It is better to have a good "single point ground". But everything I have read indicates multiport plug-in suppressors with high ratings will provide protection for almost everything but a direct lightning strike to a house. The IEEE guide has an illustration of a multiport suppressor protecting when a cable entry is too far from the power service. The impedance to surges of the wiring inside the house greatly limits the current, and hence energy, available at a plug-in suppressor.
P
phil-news-nospam
On Fri, 29 Feb 2008 02:23:56 -0500 Michael A. Terrell wrote: | snipped-for-privacy@ipal.net wrote: |> |> On Thu, 28 Feb 2008 01:45:12 -0600 bud-- wrote: |> |> | Martzloff has also written "In fact, the major cause of TVSS [surge |> | suppressor] failures is a temporary overvoltage, rather than an |> | unusually large surge." |> |> And these would not damage the TV? | | | No. Why do you think it would? if the surge suppresser clips at a | safe voltage to protect from spikes, it won't go any higher with a | overvoltage condition, but the MOV or other protection device quickly | overheats as it tries to maintain the proper voltage. If the line | voltage is high enough, it will trip the Breaker, or blow the fuse for | that AC circuit. The protective device can only dissipate a small | amount of heat before it self destructs.
This was a discussion about a suggestion tha the MOV condunction voltage should be higher than now used (330V for 120V systems). He wants to raise that voltage to avoid certain situations causing TVSS failure so the protection against spikes (above 800V) is maintained longer. My position is that the swells as high as 565V RMS could in fact cause damage to the TV. Under his proposal, these would be be suppressed. I think that is a bad idea because these voltage swells really can do damage.
P
phil-news-nospam
On Fri, 29 Feb 2008 03:53:29 -0600 bud-- wrote: | snipped-for-privacy@ipal.net wrote: |> On Thu, 28 Feb 2008 01:45:12 -0600 bud-- wrote: |> |> | Martzloff has also written "In fact, the major cause of TVSS [surge |> | suppressor] failures is a temporary overvoltage, rather than an |> | unusually large surge." |> |> And these would not damage the TV? | . | Damage to a TV obviously depends on the TV and the overvoltage. | | The IEEE guide goes on a length how the protected load can be connected | across the MOVs or connected to the incoming line. If connected across | the MOVs, the protected load will be disconnected when overheating MOVs | are disconnected on failure. I suspect that MOVs will overheat and be | disconnected before high current operates overcurrent devices. | A few plug-in suppressors will disconnect on overvoltage.
And you are saying what?
|> |> If that voltage is what the UL says is right, and tests for (I presume |> |> they have surge simulation tests under power to verify that MOV devices |> |> don't just open back up under a surge event, etc) |> | . |> | UL1449 has quite a few tests. MOVs fail by conducting. |> |> Conducting when the voltage reaches the specified level is doing the job |> expected of them. | . | The intended point was that MOVs don?t normally fail by "open[ing] back up". | . |> I would not call that a failure. | . | MOVs, like anything else, will fail. The normal way they fail is low | resistance
In they sense they no longer provide protection, that is a failure.
|> The device may not |> be usable after that event (the MOV being fused to conduct), but that is |> part of the design. | . | It isn?t a design. It is the way they work.
The design of the surge protector is to use the characteristic of the MOVs.
|> I believe UL should be testing surge protectors with respect to things |> like whether they pose safety risks. Will it electrocute me when I flip |> the switch on it? Will it break and short out when I try to plug in to |> one of its outlets? Will the cord on it fail and expose wires when it is |> handled a little roughly? Will it develop a hot spot and result in my |> house burning down when I am away or asleep? Will it explode when given |> the design voltage plus or minus the prescribed margin range? | . | Why would you think UL isn?t testing for safety risks.
I didn't say they aren't. I'm commenting about the expectations as a response to a comment about what I thought were poor expectations.
P
phil-news-nospam
On Fri, 29 Feb 2008 04:02:22 -0600 bud-- wrote: | snipped-for-privacy@ipal.net wrote: |> On Thu, 28 Feb 2008 12:11:16 -0600 bud-- wrote: |> |> |
formatting link
|> | has an illustration of a surge coming in on a cable service (pdf page |> | 40). The problem is the 'ground' wire from cable entry block to power |> | service is too long allowing a damaging voltage between cable and power |> | wires. A power service suppressor would do nothing to solve the problem. |> | |> | Cable, phone, ... other entry protectors need to protect to ground and |> | have short 'ground' wires to the earth conductor at the power service. |> | Otherwise the guide says "the only effective way of protecting the |> | equipment is to use a multiport [plug-in] protector". A N-G bond in the |> | power service also helps limit the voltage difference, particularly if a |> | power service surge suppressor is not used. |> |> If you do not have the proper common entrance for all services in one place, |> then the effectiveness of the surge protector power strip will be reduced. |> It's still better to have one than not. But it is no replacement for having |> the correct entry protection, which includes cable, phone, and power coming |> in at the same location and grounded together so voltage differences between |> these types of wiring are eliminated (at least with respect to surges coming |> in from outside on the wire). | . | A lot of houses have signal entrances too distant from power services. | It is better to have a good "single point ground". But everything I have | read indicates multiport plug-in suppressors with high ratings will | provide protection for almost everything but a direct lightning strike
Maybe almost. Definitely not all.
| to a house. The IEEE guide has an illustration of a multiport suppressor | protecting when a cable entry is too far from the power service. The | impedance to surges of the wiring inside the house greatly limits the | current, and hence energy, available at a plug-in suppressor.
Tell that (impedance of inside wiring) to some past devices I've had destroyed by lightning induced surges, or direct hits.
B
bud--
formatting link
> |> | has an illustration of a surge coming in on a cable service (pdf page
If you are talking about a direct lightning strike to a building, I specifically exclude them above. Protection includes lightning rods. If you have a tower antenna you are talking about a whole different level of protection.
If you are talking about general electronic "devices", the branch circuit impedance does not limit the voltage (although US panels and receptacles will arc over at about 6kV).
For plug-in suppressors, the suppressor clamps the voltage and the branch circuit impedance greatly limits the current.
B
bud--
. Surge suppressors are intended to protect against surges. Raising the clamp voltage is to lower unnecessary suppressor exposure to surges that do not damage connected equipment.
Surge suppressors are not intended to protect against longer duration swells or even longer duration overvoltage. Martzloff's comment above is that the major cause of failure is overvoltage, which suppressors are not intended to protect against.
If you keep the clamp voltage low, you are likely not increasing protection from swells because a swell may well kill the MOV anyway. To protect against overvoltage get a suppressor that disconnects on overvoltage.
E
ehsjr
But what you are doing in the discussion is force fitting the MOV TVSS into protecting against events that it was not designed for. It's like insisting that your umbrella protect against the rain in a hurricane. It might keep the rain off briefly, before the wind blows it apart.
Ed
P
phil-news-nospam
On Sat, 01 Mar 2008 03:12:55 -0600 bud-- wrote: | snipped-for-privacy@ipal.net wrote: |> On Fri, 29 Feb 2008 02:23:56 -0500 Michael A. Terrell wrote: |> | snipped-for-privacy@ipal.net wrote: |> |> |> |> On Thu, 28 Feb 2008 01:45:12 -0600 bud-- wrote: |> |> |> |> | Martzloff has also written "In fact, the major cause of TVSS [surge |> |> | suppressor] failures is a temporary overvoltage, rather than an |> |> | unusually large surge." |> |> |> |> And these would not damage the TV? |> | |> | |> | No. Why do you think it would? if the surge suppresser clips at a |> | safe voltage to protect from spikes, it won't go any higher with a |> | overvoltage condition, but the MOV or other protection device quickly |> | overheats as it tries to maintain the proper voltage. If the line |> | voltage is high enough, it will trip the Breaker, or blow the fuse for |> | that AC circuit. The protective device can only dissipate a small |> | amount of heat before it self destructs. |> |> This was a discussion about a suggestion tha the MOV condunction voltage |> should be higher than now used (330V for 120V systems). He wants to |> raise that voltage to avoid certain situations causing TVSS failure so |> the protection against spikes (above 800V) is maintained longer. My |> position is that the swells as high as 565V RMS could in fact cause |> damage to the TV. Under his proposal, these would be be suppressed. |> I think that is a bad idea because these voltage swells really can do |> damage. | . | Surge suppressors are intended to protect against surges. Raising the | clamp voltage is to lower unnecessary suppressor exposure to surges that | do not damage connected equipment.
The last 7 words are the part we do not agree on.
| Surge suppressors are not intended to protect against longer duration | swells or even longer duration overvoltage. Martzloff's comment above is | that the major cause of failure is overvoltage, which suppressors are | not intended to protect against.
I've read discussions and online pages to the contrary. If you have put forth your theory ahead of time, I could have recorded the locations for you.
| If you keep the clamp voltage low, you are likely not increasing | protection from swells because a swell may well kill the MOV anyway. To | protect against overvoltage get a suppressor that disconnects on | overvoltage.
The surge suppressor already does this. Sure, it can _die_ while doing this. The MOV shorts across, causing an increase in current that trips the supplementary breaker in the strip (usually integrated in the switch). There, appliance protected by one low cost device.
Maybe what should have proposed was that we use a more expensive device that integrates higher level MOVs with overvoltage sensors. If he can show that such a MORE EXPENSIVE device is worth the extra cost in the longer term, he wins. But I think he cannot. The reason ons that even a doubling of cost to make such a device (I think it is more than just that) would not produce a win for the consumer because really too few surge protectors have this issue for the total payout to not be increated by the more expensive device.
P
phil-news-nospam
On Sat, 01 Mar 2008 14:39:23 GMT ehsjr wrote: | snipped-for-privacy@ipal.net wrote: |> On Fri, 29 Feb 2008 02:23:56 -0500 Michael A. Terrell wrote: |> | snipped-for-privacy@ipal.net wrote: |> |> |> |> On Thu, 28 Feb 2008 01:45:12 -0600 bud-- wrote: |> |> |> |> | Martzloff has also written "In fact, the major cause of TVSS [surge |> |> | suppressor] failures is a temporary overvoltage, rather than an |> |> | unusually large surge." |> |> |> |> And these would not damage the TV? |> | |> | |> | No. Why do you think it would? if the surge suppresser clips at a |> | safe voltage to protect from spikes, it won't go any higher with a |> | overvoltage condition, but the MOV or other protection device quickly |> | overheats as it tries to maintain the proper voltage. If the line |> | voltage is high enough, it will trip the Breaker, or blow the fuse for |> | that AC circuit. The protective device can only dissipate a small |> | amount of heat before it self destructs. |> |> This was a discussion about a suggestion tha the MOV condunction voltage |> should be higher than now used (330V for 120V systems). He wants to |> raise that voltage to avoid certain situations causing TVSS failure so |> the protection against spikes (above 800V) is maintained longer. My |> position is that the swells as high as 565V RMS could in fact cause |> damage to the TV. Under his proposal, these would be be suppressed. |> I think that is a bad idea because these voltage swells really can do |> damage. |> | | But what you are doing in the discussion is force fitting | the MOV TVSS into protecting against events that it was not | designed for. It's like insisting that your umbrella | protect against the rain in a hurricane. It might keep | the rain off briefly, before the wind blows it apart.
That's a poor analogy.
The MOV based TVSS is most like to short circuit in a damaging event and cause the incoming breaker (the switch in the power strip, for example) to trip. The power strip might now be a usless hunk of metal and plastic, but the appliance to be protected is still protected for the duration.
P
phil-news-nospam
|> Tell that (impedance of inside wiring) to some past devices I've had |> destroyed by lightning induced surges, or direct hits. |> | If you are talking about a direct lightning strike to a building, I | specifically exclude them above. Protection includes lightning rods. If | you have a tower antenna you are talking about a whole different level | of protection.
I was talking about either direct strike or an induced strike on any of the incoming service lines.
| If you are talking about general electronic "devices", the branch | circuit impedance does not limit the voltage (although US panels and | receptacles will arc over at about 6kV). | | For plug-in suppressors, the suppressor clamps the voltage and the | branch circuit impedance greatly limits the current.
... until the breaker can trip and open the circuit if the voltage is not as high as the arc-over level.
E
ehsjr
Ok, what specific TVSS models claim to be designed to do what you stated: protect against the overvoltage in the damaging event? Or are you just trolling?
Ed
W
w_tom
Bud's own posts, including Page 42 Figure 8, say otherwise. Protectors without earth ground are not an effective solution to surges that seek earth ground.
When utilities do not enter at a common point, then a better solution is to make a lager single point ground by merging all electrodes with a buried wire. The title is "Preventing Damage Due to Ground Potential Difference". A utility demonstrates how to accomplish this in wrong, right, and preferred pictures:
formatting link
Protection is only as effective as the earth ground. Bud says otherwise to promote plug-in protectors that have no effective earthing. That 'buried bare copper wire' solution recommended to "Prevent Damage ..." makes every earthing connection both more conductive AND interconnects all to a single point ground.
Two reasons are why earthing provides protection. For even better protection, some loop a building with a buried ground wire - techniques such as halo or Ufer grounds. Effective protection is about conductivity and equipotential. That buried ground wire improves both making all appliances even better protected. Protection is only as effective as the earthing which is why high reliability facilities are obsessive about their earthing.
W
w_tom
Lightning striking utility wires down the street may be a direct strike to appliances inside a building. We install protectors to make direct lightning strikes irrelevant. 'Whole house' protectors are sized and earthed so that direct lightning strikes do not find earth ground, destructively, via household appliances. This is how protection was implemented even 100 years ago.
Lightning view utility's AC electric wires as an antenna connected to household appliances. What was proven in radio stations also applies to protecting household appliances. Protection proven 100 years ago for radio station antennas and telephone company facilities is also provided by a properly earthed 'whole house' protector. Only plug-in protectors don't do what has been proven effective for over
100 years.
Type of surge that typically overwhelms protection already inside all appliances is the direct lightning strike. We install a 'whole house' protector to make direct lightning strikes. Bud does not recommend plug-in protectors for the type of surge that typically does damage? What kind of protection is that? Profitable. Ineffective. Does not remain functional after a typically destructive surge. Appliances can be damaged by a direct lightning strike if lightning to AC utility wires is not earthed. We earth an effective protector for direct lightning strikes. We install plug-in protectors to maximized profits.
Discussion about effective protection is about making the direct lightning strike irrelevant - so that the protector even remains functional. 'Whole house' protectors earth direct lightning strikes AND remain functional. Bud admits that plug-in protectors do not do what is necessary for effective protection.
G
gfretwell
If you really want to protect your equipment you should have a very fast operating fuse, selected for ~125% of the FLA of your equipment in front of the MOV. Then while the MOV is self destructing the fuse will blow
P
phil-news-nospam
On Sat, 01 Mar 2008 18:01:51 GMT ehsjr wrote: | snipped-for-privacy@ipal.net wrote: |> On Sat, 01 Mar 2008 14:39:23 GMT ehsjr wrote: |> | snipped-for-privacy@ipal.net wrote: |> |> On Fri, 29 Feb 2008 02:23:56 -0500 Michael A. Terrell wrote: |> |> | snipped-for-privacy@ipal.net wrote: |> |> |> |> |> |> On Thu, 28 Feb 2008 01:45:12 -0600 bud-- wrote: |> |> |> |> |> |> | Martzloff has also written "In fact, the major cause of TVSS [surge |> |> |> | suppressor] failures is a temporary overvoltage, rather than an |> |> |> | unusually large surge." |> |> |> |> |> |> And these would not damage the TV? |> |> | |> |> | |> |> | No. Why do you think it would? if the surge suppresser clips at a |> |> | safe voltage to protect from spikes, it won't go any higher with a |> |> | overvoltage condition, but the MOV or other protection device quickly |> |> | overheats as it tries to maintain the proper voltage. If the line |> |> | voltage is high enough, it will trip the Breaker, or blow the fuse for |> |> | that AC circuit. The protective device can only dissipate a small |> |> | amount of heat before it self destructs. |> |> |> |> This was a discussion about a suggestion tha the MOV condunction voltage |> |> should be higher than now used (330V for 120V systems). He wants to |> |> raise that voltage to avoid certain situations causing TVSS failure so |> |> the protection against spikes (above 800V) is maintained longer. My |> |> position is that the swells as high as 565V RMS could in fact cause |> |> damage to the TV. Under his proposal, these would be be suppressed. |> |> I think that is a bad idea because these voltage swells really can do |> |> damage. |> |> |> | |> | But what you are doing in the discussion is force fitting |> | the MOV TVSS into protecting against events that it was not |> | designed for. It's like insisting that your umbrella |> | protect against the rain in a hurricane. It might keep |> | the rain off briefly, before the wind blows it apart. |> |> That's a poor analogy. |> |> The MOV based TVSS is most like to short circuit in a damaging event and |> cause the incoming breaker (the switch in the power strip, for example) |> to trip. The power strip might now be a usless hunk of metal and plastic, |> but the appliance to be protected is still protected for the duration. |> | | Ok, what specific TVSS models claim to be designed to do | what you stated: protect against the overvoltage in the | damaging event? Or are you just trolling?
Apparently most all of them ... either designed that way or just happen to operate that way. Otherwise the previously mentioned paper would not have needed to be written.
E
ehsjr
I asked for specific models. Your answer does not contain a specific model. So you are trolling after all.
Ed
B
bud--
. You are disagreeing with Martzloff, who has done a lot of research on surge protection an has numerous published papers. The same immunity has also appeared elsewhere such as a PCMagazine review of plug-in suppressors. .
. Contrary - overvoltage is the major cause of failure? - you are again disagreeing with Martzloff.
Contrary - not intended to protect against swells and overvoltage? - provide a source that says plug-in suppressors are intended to protect against swells and overvoltage. Like maybe specs from few manufacturers that Ed asked for.
"Put forth your theory ahead of time" - apparently a new newsgroup requirement? .
. By the time current reached well over 15A required to trip a 15A breaker in a short time, the MOV would be toast. UL has required since 1998 that thermal disconnects be provided to disconnect overheating MOVs. Or fuses as Greg suggests, but selected by the manufacturer which can have operating characteristics closely matched to the MOVs, may also open. It is unlikely that protection would come from a breaker.
Repeating: "The IEEE guide goes on a length how the protected load can be connected across the MOVs or connected to the incoming line. If connected across the MOVs, the protected load will be disconnected when overheating MOVs are disconnected on failure." Similar comments are in the NIST guide.
Your response was "And you are saying what?"
What: that is the probable protection route indicated in both guides if a plug-in suppressor can provide protection from overvoltage. Both guides make clear not all plug-in suppressors are wired to disconnect the protected load with the MOVs. .
. Repeating: "To protect against overvoltage get a suppressor that disconnects on overvoltage." They disconnect the load and MOVs. .
. "He"? Is "he" Martzloff? I have never seen Martzloff indicate a MOV based surge suppressor should protect against swells or overvoltage.
The "IEEE Recommended Practice for Powering and Grounding Sensitive Electronic Equipment" (Emerald book) does not indicate plug-in suppressors are an effective means of protecting against swells or overvoltage.
Perhaps you could use a plug-in suppressor with overvoltage protection built in, as above.
If you want to use failure of MOVs to protect your equipment I would suggest a suppressor from a reputable manufacturer where the manufacturer says the suppressor will protect from swells and overvoltage. Given hype, I suggest using a device where the manufacturer also has a warrantee on protected equipment.
Saying plug-in suppressors should protect against swells and overvoltage they are not designed for does not make them effective.
======================== Or perhaps you could use a device the Emerald book indicates might be effective. For houses that would be a UPS. But make sure the manufacturer says the UPS will protect against swells and overvoltage.
B
bud--
. w_ apparently believes a strike to a utility line down the street with multiple paths to ground, a distant connection and coming through controlled entrance to a house is the same as a strike to an adjacent tower antenna sticking far above anything else and connected to sensitive electronics in the house. .
. UL listed suppressors have MOVs from H-G, N-G, H-N. That is all combinations and all possible surge modes. w_ has never explained how a common mode surge coming in on a power service gets past the N-G bond required at all US services. Past the service the surge is transverse mode. .
. ?Direct lightning strike? is ?direct strike to a building? in the beginning quote. Apparently w_ thinks that a service panel suppressor provides that protection, without lightning rods. w_ lives in a fantasy world. .
. I admit they do not protect against a ?direct lightning strike to a building?. What a radical idea.
B
bud--
. The illustration in the IEEE guide has a surge coming in on a cable service. There are 2 TVs, one is on a plug-in suppressor. The plug-in suppressor protects TV1, connected to it.
The point of the illustration for the IEEE, and anyone who can think, is "to protect TV2, a second multiport protector located at TV2 is required." What a radical idea.
w_ says suppressors must only be at the service panel. In this example a service panel protector would provide absolutely *NO* protection. The problem is the wire connecting the cable entry block to the power service ?ground? is too long (not a "single point ground"). The IEEE guide says in that case "the only effective way of protecting the equipment is to use a multiport protector." This is the same as what is quoted from me at the top. .
. w_ has a religious belief (immune from challenge) that surge protection must use earthing. Thus in his view plug-in suppressors (which are not well earthed) can not possibly work. The IEEE guide explains plug-in suppressors work by CLAMPING the voltage on all wires (signal and power) to the common ground at the suppressor. Plug-in suppressors do not work primarily by earthing (or stopping or absorbing). The guide explains earthing occurs elsewhere. (Read the guide starting pdf page 40). .
. I promote only accurate information. w_ promotes religious dogma. .
. From
formatting link
Grounded Ring: A grounded No. 2 wire, installed around all four walls inside a small building, at an elevation of approx. six inches below the ceiling. They are used around transmitter equipment. How would a halo ground help? Perhaps w_ could learn the proper term.
Both the IEEE and NIST (below) guides say equipotential of the ground references for power, telephone, cable requires a ?*short* connection from the phone and cable entrance protectors to the earthing wire at the power service.
Everyone agrees earthing is a good idea. The question is whether plug-in suppressors work. The IEEE guide says plug-in suppressors are effective.
So does an NST guide (written by Martzzloff but aimed at the unwashed masses) at:
formatting link
the sources.
There are 98,615,938 other web sites, including 13,843,032 by lunatics, and w_ can't find another lunatic that says plug-in suppressors are NOT effective.
Simple questions never answered:
- Why do the only 2 examples of protection in the IEEE guide use plug-in suppressors?
- Why does the NIST guide says plug-in suppressors are "the easiest solution"?
- How would a service panel suppressor provide any protection in the IEEE example, pdf page 42?