On Mon, 28 May 2007 12:29:32 -0400 snipped-for-privacy@aol.com wrote: | On 28 May 2007 13:17:47 GMT, snipped-for-privacy@ipal.net wrote: | |>On Mon, 28 May 2007 00:59:50 -0400 snipped-for-privacy@aol.com wrote: |>| On 28 May 2007 04:34:44 GMT, snipped-for-privacy@ipal.net wrote: |>| |>|>| No the ground needs to be #12 copper and insuilated. |>|>
|>|>I didn't notice where the OP had said he's avoiding ground or using a |>|>smaller ground. But it's a good thing you caught that to make sure he |>|>does this right. |>| |>| |>| UF is really not one of the required wiring methods. 680.21 (pool |>| motors) only allows "rigid metal conduit, intermediate metal conduit, |>| rigid nonmetallic conduit, or Type MC cable listed for the location" |>| and since MC is not listed for burial you are left with conductors in |>| a conduit. The normal installation is rigid non-metalic conduit. (grey |>| PVC) with THHN/THWN conductors. |>
|>UF is not required, or not allowed? | | The ground is not "insulated"
Interesting. So the risk is that by not be "insulated" (e.g. the UF jacket does not qualify as insulation), the ground could in certain cases end up being energized in there, and leave someone standing in water touching something grounded by that wire with that tingly feeling (or wore). So in effect we really want what amounts to an isolated ground.
|>| I hope our OP also knows about the bonding requirements. All metal and |>| equipment that is within 5' of the water or part of the cirtculation |>| system need sto be bonded together with minimum 8 ga solid copper |>| wire. That includes pumps, heaters, ladders, rails, diving board |>| supports, any other metal within 5' like screen cages, door or window |>| frames and the steel in the concrete shell. In 2005 that also picked |>| up deck steel within 3' of the water. In 2005 you had to provide that |>| bonding for the deck even if it was pavers set in dirt with a 12x12 |>| 8ga copper wire mesh out 3'.. |>
|>Stranded is not allowed? Or does use of stranded require a larger size? | | 680.26 specifically says "solid". It is a corrosion issue.
Larger wire is harder to find in solid.
Question: If I have 7 wires of 8 ga. each, does that make a greater corrosion risk? If not, could stranded by OK (by the spirit, if the wording hasn't considered the case) if each strand is at least 8 ga.?