Equations?

OK...I know this is something I should know, but I don't. I have 4160 entering the site. I need a 480 3 phase at 200 amps, and a second panel, 120/208 3 phase 125 amp.

How do I calcultae kVA on the 4160/480 xfmr? And how do I calculate the kVa on the 480/208 xfmr?

Reply to
terryh
Loading thread data ...

try volt-amps =voltage*current* root(3) in both cases.

1000volt-amps =1KVA
Reply to
Don Kelly

Huh?

Why the "root(3)?"

VA can be determine by taking each phase voltage to neutral and multiplying by the current. If the phase currents are the same you just take one current and multiply by 3.

Reply to
<nni/gilmer

If you have individual phase voltages and currents, that is perfectly true. But if all you have is line-line voltage, then you'll find that phase voltage is line-line/sqrt(3).

So...

3*Vphase*Iphase = 3*(Vline/sqrt(3))*Iphase = Vline*Iphase*sqrt(3)

That's for a wye connected load. You can do a similar calculation for delta-connected loads but its the Iphase = Iline/sqrt(3)

daestrom

Reply to
daestrom

I should have said root(3)* line voltage*line current or 3*phase voltage* phase current Both are valid for star or for delta. Very often you only have access to 3 terminals so that only the line values can be measured.

Reply to
Don Kelly