Fuses and branch circuits

Aug 22, 2006 1 Replies

The answer in the UK is that branch circuit fuses (BS1361) have a higher breaking capacity (16.5kA) than fuses used on appliances (BS1362, 6kA).

So if you used a BS1362 fuse in a branch circuit which had a prospective short circuit current greater than 6kA, then the fuse might fail to break the current flow on a short circuit resulting in serious damage (or fire) in wiring, and/or the fuse might explode damaging the holder, because you are exceeding its breaking capacity.

I don't know for sure if the reason in your case is the same.

Why are some fuses not rated for use on branch circuits? I'm looking at using a 3 amp midget fuse and it says "not designed for branch circuit use".



Thanks.